Strange test results on an old ring:

L-L 0.14 ohms
N-N 0.15 ohms
E-E 1.12 ohms

L-N (this is where it gets weird):
1st d/skt 0.07 ohms
2nd d/skt 0.08 ohms
3rd d/skt 0.21 ohms
4th d/skt 0.36 ohms
5th s/skt 48 ohms!
6th d/skt 48 ohms!
7th d/skt 48 ohms!
Spur d/skt 48 ohms!

WTF!? This was the end of the day, so I didn't have much time to investigate. After checking the connections I found one L and one N not connected in the 6th d/skt, so reconnected them thinking that might solve the prob, but got the same readings. But even so, I don't get how one half of the ring can be affected, while the other half isn't.

Is it the outlets? Anyone got an idea??

Getting back to this first thing tomorrow...

Cheers
 
You've stated its a ring... just because you get an end to end reading dosn't prove anything, try the ELI reading at the fuseboard and then at each point to see if you have a small ring with extensive radials attached it should give you prgressive slightly higher readings up to the mid point any unusual readings may show multiple sockets on a radial a practice ofen seen in the olden days.
Also be aware some terminal screws are coated with to stop the metal oxidising and this can also mess reading up.
 
How can it be radials when I get the end to end results? Didn't have time for ELI, so will do that and check each outlet thoroughly first up.
 
Make sure it is a ring first.
If it is a ring then your end to end on e is way out and needs addressing.
For the L-N readings if you are taking readings through a socket adapter I would suggest dirty contacts / loose termination on 3 and 4 and then at 4 or 5 one of the live conductors is twisted to the outgoing but loose in the terminal. Disconnect and remake the connections and check again or check at the back of the sockets.
 
Your meter may be faulty. By your readings at the cu l-l and n-n =21.5 metres length of ring. Your e-e reading = 103 metres. Did you short L to n In out legs of rings at board then l-n at each socket? If so you should have a reading of 0.075 ohms at each socket. Do the same with L&E cables and you will find the fault when you get an odd reading at a socket outlet. There is a definite problem with the cpc connections.
 
Glad you got it sorted :) but are these figures correct ?
5th s/skt 48 ohms!
6th d/skt 48 ohms!
7th d/skt 48 ohms!
Spur d/skt 48 ohms!

Thats a massive reading at the sockets or should it read .48?
 
Glad you got it sorted :) but are these figures correct ?
5th s/skt 48 ohms!
6th d/skt 48 ohms!
7th d/skt 48 ohms!
Spur d/skt 48 ohms!

Thats a massive reading at the sockets or should it read .48?
I should get your meter re calibrated. Do as prescribed in guidance note 3 check r1 plus r2; or take r2 readings. Make sure you are happy before signing off any certificates. I would be worried to have such high readings without an obvious reason for this. Good Luck
 

Reply to Weird continuity results on ring in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

  • Question
They ought to be able to check for the voltage going completely off using one MCB off at a time to confirm that. That would be my assumption...
Replies
9
Views
759
  • Question
Some more information. I probably dont need 100 amps with a 1000v cable at the moment, but i want to replace like for like, and future proof it...
Replies
15
Views
3K
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2
Replies
45
Views
5K
Ah so sounds like DNO not involved after all.
Replies
6
Views
2K
  • Question
and we can see wet-pants knows about the 150mm clearance from electrical services. ????
2
Replies
44
Views
11K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks