- Joined
- Feb 18, 2008
- Messages
- 118
- Reaction score
- 10
Hi I had a call out tonight where the tenant said she was getting a shock from her hot and cold taps and also her sink in the kitchen.Her worktop had been changed today and when I looked under the sink the usualtrend of joiners/plumbers of cutting earth cables had taken place.the pipes where all cross bonded but a cable from one pipe was lying loose and also a6mm earth from a double socket underneath for dishwasher and washing machine had also been cut.testing between the tap/sink I was getting20v however when I switched on the dp switch for the double socket it was jumping up to 134v.why was this not lifting the rcd or mcb?zs on the sockets was 0.76.I was getting on earth continuity of 0.34 between fusebox and the pipes/sink/tap.when I connected the 2 cut earth cables back up to the sink the voltage dissapeared.I know about the need to bond all pipework so that their potentiol is the same but could someone explain this one to me please?