I've been asked to install and American TIG welder in a workshop at a site where i do some more normal commercial works.

The Welder requires a 400v Supply (no problem as TP supply nearby) but the current DB is a Hager unit for whichi can only find max MCB's of 63A. this welder requires something closer to 80A per phase.

My thoughts we're can i split the supply feed prior to the DB (or drop extra feeds out the bottom of the DB incomer) and send a second set of feeds into a TP 100A Switch Fuse ? this would then in turn run 25mm 3 core SWA (10 metres max) and down to a another Switched Disconnect located closer to the Welder and then hardwired into this?

or have a missed something vital or even overcomplicating things?

FFYI - the welder is a Miller Syncrowave 351 and the manual can be found here 351 Manual

This needs to be done friday evening after the workshop has closed to minimise downtime.

Cheers in advance!
 
Last edited by a moderator:
All sorted now.


Basically it's a 2 phase welder. It requires two phases (live) at 80A rated and then an earth. The supply board has a maximum Amp of 63A per phase MCB. So it cannot handle the current. The manufacturer suggested either exchanging the welder for an Invertor 3 phase version which runs at a meagre 13a per Line or replace the DB with one which can handle higher loads.

Appreciate the help though.
 

Reply to Welder Installation in the Electrician Talk | All Countries area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
305
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
825
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
916

Similar threads

  • Question
Good point, I was assuming an up-front RCD is for fault protection within DB, etc, and to cover for a failed RCBO for fault conditions, not as...
Replies
6
Views
2K
When I was on the electric board We had a pair of pillocks connect a housing estate to a very large genset, the n lead was in two parts and not...
2
Replies
28
Views
4K

Search Electricans Forums by Tags

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top