So they are still on separate circuits?

How will you safely isolate one of the circuits, when it is electrically connected to another that is still energised.

That is potentially very dangerous, and further will cause you problems when your consumer unit is eventually upgraded to RCBO’s/AFDD’s.

Unless I’ve misunderstood something, your installer is clueless.
 
You didn’t miss understand. Apologies, I didn’t take the time to explain the solution properly. The original dedicated HW/CH supply has been moved across to the RCD side of the board and the UFH is now part of the same circuit. I really appreciate you following up on my vague post 😳
 
Last edited:
That has not solved the issue, you still have an incredibly dangerous situation which could lead to serious injury or damage to your heating system.

It sounds like you still have two circuits connected together via your heating controls, all of the heating controls should ideally be fed via a single switched fuses spur so that there is only one fuse protecting the whole thing.
Currently you must have two fuses protecting the heating system.
Apologies, I didn’t take the time to explain properly. The original dedicated HW/CH supply has been moved across to the RCD side of the board and the UFH is now part of the same circuit. Thanks for following up though, Much appreciated.
 
Apologies, I didn’t take the time to explain properly. The original dedicated HW/CH supply has been moved across to the RCD side of the board and the UFH is now part of the same circuit. Thanks for following up though, Much appreciated.

So both the UFH and the rest of the heating controls are now fed via a single fuse?
Or are the UFH and the other controls now fed from two different connections to the same circuit?
 
So both the UFH and the rest of the heating controls are now fed via a single fuse?
Or are the UFH and the other controls now fed from two different connections to the same circuit?
The UFH and the rest of the heating controls are now fed via a single fuse. So a 6 Amp CB on the RCD side of the consumer unit to a switched fused spur (with 3amp fuse) which supplies the heating controller and all the components within the system including those on the underfloor heating manifold.
 

Reply to Wet UFH Tripping RCD in the Electric Underfloor Heating Wiring area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock