Faced with a switch drop suffering from having architrave screwed over it. Not overly experienced in domestic work so looking for some options on how to deal with it.

IMG_20210316_172157.jpgIMG_20210316_172200.jpgIMG_20210316_172204.jpgIMG_20210316_172148.jpg

My first thought was to have the contractor take the architrave off & then to hack out and joint behind the architrave, but obviously the reason there's a screw in the cable in the first place is that the harmonised colours cable is out of the prescribed zones.

And then there's the various textured finishes, picture rail, cornice...
 
I'm lost, where is this screw through the cable in relation to the switch drop.
Under the paint. Cable leaves the switch out of the side and runs up behind the architrave.

Pretty much a dead short SL-E.

If someone was reckless enough to disconnect the cpc, energise the SL, and then waved a non contact tester at the potentially live door frame the beeps would stop part way down the frame.

Previous electrician blames the chippy but it is post 2004 colours so the cable should not be where it is.
 
So it runs behind the door frame or the dado rail. Are you trying to apportion blame or find a solution to repair it.
 
If I were tasked with this then the cable needs replacing as in #11. Any repairs/making good would not be my concern.
 
Quinetic is the answer. diss. the switch cable at the light. no decor disturbed. no cable out of zone. winner.
 
I think the screw / nail is in the architrave, but I can't confirm it's that direction and not from the casing without having the paint off. Definitely not from the picture rail.

If I were tasked with this then the cable needs replacing as in #11. Any repairs/making good would not be my concern.
Taken off properly there would be very little making good to do, score the paint with a knife where the architrave meets the frame, a good sharp wood chisel to take the architrave off and a bit of caulking to tidy it up when it goes back.
 
Taken off properly there would be very little making good to do, score the paint with a knife where the architrave meets the frame, a good sharp wood chisel to take the architrave off and a bit of caulking to tidy it up when it goes back.
but he'd still be left with a cable outside prescribed zone.
 
still think a quinetic switch (and receiver) would be the ideal solution. saves repair to cable, decor repair, and eliminates the outof zone issue.
 
the costof a qiunetic switch and receiver would be less that the labour costs of fixing the existing cable and redecoration.
 
Agreed.

I'm surprised by property manager and or landlord decisions every week, so I wouldn't put it past them to suggest a pull cord next to the pendant as a budget solution
If they do, suggest doing it in surface mini trunking instead...... another carp idea!!!....but it shows you're thinking off the same page as them. ?
 
Is there no way to lift a board above it and rewire it? It could only be a few metres of cable from the light to the switch. I wouldn't be burying a joint back behind it again.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

DJAndy

Arms
Joined
Location
Loughborough
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
What are my options here?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
33
Unsolved
--

Advert

Thread statistics

Created
DJAndy,
Last reply from
nicebutdim,
Replies
33
Views
3,147

Advert

Back
Top