House is TNCS, remote garage has a 60A supply that is TT'd and contains supplies for an adjacent (defunct) swimming pool, and a gas boiler.
SWA enters a plastic box, earth is left in the box whilst L-N enter metalclad CU.
Zdb is 0.2 ohms - probably due to the gas bonding in the house.
In theory a supply for TT shouldn't enter a metalclad enclosure unless its RCD protected, but because the Zs is so low the garage supply fuse will blow if there was a fault to the enclosure.
Should I include this in an EICR and if so what category?
SWA enters a plastic box, earth is left in the box whilst L-N enter metalclad CU.
Zdb is 0.2 ohms - probably due to the gas bonding in the house.
In theory a supply for TT shouldn't enter a metalclad enclosure unless its RCD protected, but because the Zs is so low the garage supply fuse will blow if there was a fault to the enclosure.
Should I include this in an EICR and if so what category?