What do I need for a emergency lighting cert | on ElectriciansForums
Discuss What do I need for a emergency lighting cert in the UK Electrical Forum area at ElectriciansForums.net
R
Rauer
Hi been asked to do an emergency lighting cert for a company I do a fair amount of electrical work for , is there any particular course or registration that I need?
BS 5266 says where national regulations do not apply the following checks shall be completed:
Daily:
Visual confirmation of LED indicators, central battery cubicles, self-contained units etc.
Monthly:
Duration testing (Partial Duration)
Check condition of fittings, present? Clean? Functioning correctly?
Annually:
Duration testing (Full Duration)
The reason for partial duration on the monthly test is to limit the risk posed by draining the batteries do. If there was a true emergency just after you had just completed a full duration test the emergency lights would not have had sufficient time to fully recharge.
BS5266 says a log book shall be kept on the premises in the care of a responsible person appointed by the occupier/owner and shall be readily available for examination by any duly authorized person.
The log book shall be used to record at least the following information:-
  1. Date of commissioning including certificates
  2. PIR dates
  3. Dates & brief service details, inspection or test
  4. Dates & brief details of any remedial works
  5. Dates & brief details of any alterations to the system
  6. If any auto test devices exist, the main characteristics and the mode of operation shall be described.
Reply to What do I need for a emergency lighting cert in the UK Electrical Forum area at ElectriciansForums.net
The company Liteplan do replacement modules: Liteplan – The UK's largest emergency lighting component supplier. - https://www.liteplan.com/ This...
Or a combined fitting in each row.
nicebutdim