Hi All.
Background: House with standard consumer unit with MCBs, no RCD protection. All wiring PVC T&E, earths to all circuits, PME supply. Extension built few years ago, 2 x RCBOs added in to cover new circuits.
An approved spark did the wiring on behalf of the builder. I noticed the certs didn't look like official certs even though he was registered. Mentioned this and got replacement certs, said he had run out. Mmm. Also, no stickers for new/old wiring colours and RCBO testing - minor point, but should have been done.
I looked at the bonding recently, and its under-sized - wish I'd realised this at the time but hey ho. This obviously means that any work by the electrician should not have been carried out.
Now I want to replace the consumer unit with a new one and use RCBOs for all circuits. Now I'm 17th qualified but not a spark. My issue is that I'm not allowed to replace my consumer unit, but the guy who did the work above would be. Obvously I shouldn't do the work myself, but my installation would be a lot safer after the work was done.
Sorry for the lengthy post, but interested in people's comments. I realise I will get slated as a DIYer so I'm prepared!
Background: House with standard consumer unit with MCBs, no RCD protection. All wiring PVC T&E, earths to all circuits, PME supply. Extension built few years ago, 2 x RCBOs added in to cover new circuits.
An approved spark did the wiring on behalf of the builder. I noticed the certs didn't look like official certs even though he was registered. Mentioned this and got replacement certs, said he had run out. Mmm. Also, no stickers for new/old wiring colours and RCBO testing - minor point, but should have been done.
I looked at the bonding recently, and its under-sized - wish I'd realised this at the time but hey ho. This obviously means that any work by the electrician should not have been carried out.
Now I want to replace the consumer unit with a new one and use RCBOs for all circuits. Now I'm 17th qualified but not a spark. My issue is that I'm not allowed to replace my consumer unit, but the guy who did the work above would be. Obvously I shouldn't do the work myself, but my installation would be a lot safer after the work was done.
Sorry for the lengthy post, but interested in people's comments. I realise I will get slated as a DIYer so I'm prepared!