Yes,,BUT,,

As James has said, the local distribution cable leaving the substation has protection of 300a or whatever is appropriate for the cable.

Here's the BUT,,
When the cable to the property / house is taken off that cable it's CSA is dramatically reduced at 16mm² or 25mm² or whatever, so the 300a would not be suitable protected and in the U.K that joint is not in a position where it could be.

It would be the same as having a 20a protected radial wired in 2.5mm² with 0.5mm² cables directly joined onto it along the way, you'd need to protect those.
10mm concentric in our house and most of the surrounding area. Always found it interesting that the tails are bigger than the incoming cable.
 
So on a kettle, is the fuse there to protect the appliance lead?
The fuse in the plug is there to protect the appliance lead from overload or fault current.

There's an appliance load drawing on a cable, if load draws too much, fuse at the start of cable breaks, stopping flow, protecting appliances cable.

To protect against overload the fuse needs to disconnect the appliance from the supply, so whether it is at the beginning or end of the cable it doesn't technically matter.

This is only true of overload protection, for fault protection the fuse needs to disconnect the fault from the supply, a fault can occur anywhere in the cable so the protection needs to be at the beginning.

Load draws on double socket, draws too much, breaker in CU breaks to protect 2.5mm wiring into socket.

Yes, but equally if there was a fuse built in to the socket then that would protect the 2.5mm wiring exactly the same.
Entire load of house pulls too much on 25mm tails, main fuse goes.

Yes, and because that fuse has operated the overload is disconnected from the cable upstream of the fuse.
So it should then stand to reason that cut out is there to protect the installation wiring not the main incomer?

It is put there to protect the incoming service cable, it is not put there to protect the installation wiring.
It will in reality protect the installation wiring but it is not installed for that purpose and we are not allowed to use it for that (except for meter tails up to 3m long)
 

Reply to What does the main fuse protect? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
376
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
944
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Replies
7
Views
512
I can imagine it just disappearing (loudly) under short circuit conditions, then the resulting blast/plasma etc. casing the busbars to flash over...
Replies
13
Views
705

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top