Hello,

I wanted to know what others would do with this situation.

Currently the house that I am going to rewire and replace CCU on has (starting at distributers cut out installed externally in box) from 60A fuse/service head are 16mm tails to meter, from meter 16mm tails to 100A DP isolating switch, from DP 10mm MICC to existing CCU approx 5 meters away.

Am going to replace the 10mm MICC with either either 16mm or 25mm SWA (max. current carrying capacity of 10mm PVC sleaved MICC clipped dircet =77A)

As the tails from DP to CCU are over 3m in length, I have to install a SP&N switchfuse within the first 3 meters. I will prob. remove DP isolator in external box and put switchfuse in there if there is room and ownership of box cannot be 100% established.

So finally to my question - if the distributers cut out is 60A what rated fuse would you put in the switchfuse?

All suggestions welcome.

Thanks.
 
Re: What fuse rating in SP&N switchfuse would you use on domestic supply with 60A cut

Some may say 40A to achieve discrimination.
I'd just use 60A anyway to give the consumer the most current available.
 
Last edited by a moderator:
Re: What fuse rating in SP&N switchfuse would you use on domestic supply with 60A cut

There is no need or requirement to provide discrimination with the suppliers fuse
You size your fuse to your own installation

If you tried to discriminate,you would probably need a fuse at least half the rating of the suppliers and even then,discrimination would be hit and miss which would go first
If either goes the effect is still going to be the same ie loss of supply
 
Re: What fuse rating in SP&N switchfuse would you use on domestic supply with 60A cut

How many boards do you see that have the potential of drawing 100A which have 16mm tails to a 60A distributors fuse. At the end of the day it is safe as the fuse is rated to the tails
 
Re: What fuse rating in SP&N switchfuse would you use on domestic supply with 60A cut

Many thanks for all of your replies. So I'm going to use a 60A in the switchfuse, and understand the view to keep the 10mm MICC, calcs ok etc. Problem is that the OSG says (2.2.3 page 17) min cable size should be 25mm². Other than future distributor upgrades I cant see why this is stated? This doubt could be my misinterpretation of the word ‘should’ (the minimum cable size should be 25mm²)….. it doesn’t say ‘must’!

Thanks again.
 
Re: What fuse rating in SP&N switchfuse would you use on domestic supply with 60A cut

The tails only need to be 25mm from the meter to the first piece of the consumers switchgear , after being fused down the sub-mains can be a smaller sized cable to the consumer unit.
 

Reply to What fuse rating in SP&N switchfuse would you use on domestic supply with 60A cut out in the Domestic Electrician Forum area at ElectriciansForums.net

Similar Threads

Yes the first bit is just standard wiring, TNS lead cable into cut-out, cut-out to meter, meter to DP isolator, top of isolator is sealed as per...
Replies
8
Views
945
The cable needs protecting the same as if a load was connected on the far end of it, rather than a generator, except that it must not share a RCD...
Replies
7
Views
2K
I have no experience of a DNO refusing to reconnect an existing installation after carrying out any work to their equipment. However in my...
Replies
20
Views
12K
davesparks
D
  • Question
I know you’ve all be waiting in suspense for the next exciting update in this story. I promise this one will be much shorter! The OH was back at...
Replies
21
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks