LlandrilloSpark

Hi fellas

Can anybody think of a reason why a new RCD which ramps at 28mA in one installation trips at 17mA in another?, is it a supply problem?, on the X1 test on 0 degrees it trips in 31ms but on 180 degrees I get noS ?, tester is a megger RCDT 320

Cheers
 
There are lots of variables that affect RCD performance.

The main one is whatever is on the load side biasing the mechanism electronics, try a test with it disconnected. Minor differences can be caused by everything from the Voltage, Ze, Zs, noise or currents on the earthing/bonding, other parallel ccts, temperature of RCD, ditto your tester, the charge in the batteries, and even if the RCD case is under stress in some way.

Had a pdf on this somewhere, will try to look it out.
 
There are lots of variables that affect RCD performance.

The main one is whatever is on the load side biasing the mechanism electronics, try a test with it disconnected. Minor differences can be caused by everything from the Voltage, Ze, Zs, noise or currents on the earthing/bonding, other parallel ccts, temperature of RCD, ditto your tester, the charge in the batteries, and even if the RCD case is under stress in some way.

Had a pdf on this somewhere, will try to look it out.


Another reason to always do your RCD device testing at the load terminals of the device itself and not downstream at say a socket outlet. Your testing the ''Device'', NOT the circuit!! Your other specified BS7671 circuit testing had done that already, .....Well i hope anyway!! lol!!!
 
Thanks for the replies fella's, interesting, I remember being taught to test an RCD on a circuit, this appears to be when i have most problems with them, so on new installs i often put a socket on a 16A breaker next to the ccu if i have a spare way, i use this for the rcd testing and have no trouble.
 
Thanks for the replies fella's, interesting, I remember being taught to test an RCD on a circuit, this appears to be when i have most problems with them, so on new installs i often put a socket on a 16A breaker next to the ccu if i have a spare way, i use this for the rcd testing and have no trouble.

It's fine to ''check'' an RCD at say a socket outlet on it's circuit, but when it comes to doing formal testing of the RCD device then that should always be at the device itself!! There's no reason to do what you do with a temporary socket....

I don't know who told you or taught you, to do your formal testing of RCD devices downstream, but if you check with any of the manufacturers, they will tell you differently.
 

Reply to What in an installation can make RCD's trip at 17ms when, its not faulty? in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
853

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top