RCD stands for "residual current device" and it can be one of several styles, but basically it looks at the current going out on the line/live wire, and the current returning on the neutral wire. Those should match, and any difference means something is going astray.

Worst case it is somebody getting an electric shock by touching live while they are in contact with earth (either metalwork in the house, or really the ground outside) and that is the stray path for the current.

The 30mA = 0.030A is the maximum trip value of stray current which, while painful, is unlikely to be fatal.

These days supply to any out building, garage, etc, should be on a RCD protected circuit, but older installations (or those done badly by "dodgy Dave" from the pub) might not have it.

Can you post a photograph of your consumer unit (CU = fuse box) and anything similar in your shed? Folks on here might be able to tell by looking at what is fitted, etc.

tldr' a safety device against electric shocks
 
RCD stands for "residual current device" and it can be one of several styles, but basically it looks at the current going out on the line/live wire, and the current returning on the neutral wire. Those should match, and any difference means something is going astray.

Worst case it is somebody getting an electric shock by touching live while they are in contact with earth (either metalwork in the house, or really the ground outside) and that is the stray path for the current.

The 30mA is the maximum trip value and is 0.03A which, while painful, it unlikely to be fatal.

These days supply to any out building, garage, etc, should be on a RCD protected circuit, but older installations (or those done badly by "dodgy Dave" from the pub) might to have it.

Can you post a photograph of your consumer unit (CU = fuse box) and anything similar in your shed? Folks on here might be able to tell by looking at what is fitted, etc.

tldr' a safety device against electric shocks
Thanks for the quick reply!

I don't have a consumer unit in the shed. The plan was to just run an extension lead out to the shed whenever I need to use the light?
 
I don't have a consumer unit in the shed. The plan was to just run an extension lead out to the shed whenever I need to use the light?
You should always have RCD protection for any mains feed going outside. Your house might already have that, but you really should check it is there.

Also it should have a self-test button that you can use to verify it really is working. That will trip out everting fed by it, so make sure everyone knows you are going to test it and that PCs are shut down, TiVo boxes not recording anything important, etc, when testing.

They should be tested roughly twice a year in most cases, but most never are :(
 
Thanks for the quick reply!

I don't have a consumer unit in the shed. The plan was to just run an extension lead out to the shed whenever I need to use the light?
Maybe it would be handy to see the fuse box inside my house in this case?
Thanks for the quick reply!

I don't have a consumer unit in the shed. The plan was to just run an extension lead out to the shed whenever I need to use the light?
 

Attachments

  • [ElectriciansForums.net] What is a 30mA RCD?
    20210210_151707.jpg
    280 KB · Views: 115
You should always have RCD protection for any mains feed going outside. Your house might already have that, but you really should check it is there.

Also it should have a self-test button that you can use to verify it really is working. That will trip out everting fed by it, so make sure everyone knows you are going to test it and that PCs are shut down, TiVo boxes not recording anything important, etc, when testing.

They should be tested roughly twice a year in most cases, but most never are :(
Can you tell by looking at this if there is rcd protection?
 

Attachments

  • [ElectriciansForums.net] What is a 30mA RCD?
    20210210_151707.jpg
    280 KB · Views: 103
Maybe it would be handy to see the fuse box inside my house in this case?
The sockets seem to be on RCD protection so that is good. However, one entry on the non-RCD side appears to say "spurs" which could be many things including odd sockets.

You can get socket testers that have a RCD test button, such as this:

If you test whatever you plan of plugging the extension lead in to it will quickly tell you if it is on your protected side (power trips off) or not.
 
Just to add, if you are thinking of putting in a semi-permanent extension lead make sure you use outdoor rated cable. If you can safely run it around walls/fence/etc so no trip hazard and not needing buried, you can use cable such H07RN-F rubber insulated stuff, for example:
 
The sockets seem to be on RCD protection so that is good. However, one entry on the non-RCD side appears to say "spurs" which could be many things including odd sockets.

You can get socket testers that have a RCD test button, such as this:

If you test whatever you plan of plugging the extension lead in to it will quickly tell you if it is on your protected side (power trips off) or not.
Thank you, I will look into these socket testers just to be sure!
 
So all I have to do is wire the live & neutral in the plug for the batten and I am safe to run an extension lead to the shed to power it?
Yes, but really it should have a 3A fuse for a light, and also make sure the clamp is gripping the overall white sheath of the lamp's cable.

Also please remove the paper instructions! I have seen plugs inserted for years with the paper still on :(
 
So to clarify, If I plug my extension lead & batten into an indoor socket and press the black button should it cut the power to the socket?
Yes. That button diverts 30mA of current which should be detected by the RCD causing it to trip (so all of those sockets go off).

Socket testers are a good thing to have for general checking of stuff, but they cannot be completely trusted. Basically if they say there is a fault, there definitely is. But if they say all clear it might not really be so. The one I linked to is one of the better ones, but obviously still not going to match a professionals' test equipment at around 20 times the price.
 

Reply to What is a 30mA RCD? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
290
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
276
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
354

Similar threads

  • Question
Thank you for taking the time to help explain this - much appreciated
Replies
7
Views
825
Glad you got it sorted.
Replies
9
Views
567

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top