If I turn off the breaker and measure the voltage across the breaker (upper and lower screws), the voltage is around 180 volt. If I measure the breaker's upper screw and the grounding bar of the breaker box, the voltage is 220.

What is the actual voltage and why is the discrepancy? Thanks.
 
In normal electrical testing procedures, testing for voltage across a circuit breaker is a meaningless test.

The lower screw of the breaker is connected to the live wire of the circuit wiring. This live wire may or may not have a connection to the neutral via something that's plugged into or connected to that particular circuit. If the circuit has no load connected ie there's nothing plugged into it then that live wire will be 'floating' and you'll get no voltage or a meaningless voltage shown when you test. If there is a load on the circuit you'll see a result on your tester close to the supply voltage but it still won't mean anything.

Testing between the circuit breaker screw and the grounding bar is a far more meaningful test, it will tell you the difference between the voltage at the screw and the voltage at the ground bar which should always be at 0v.

Whenever you test a voltage with a tester it will give you the difference in voltage between the two points you're testing. To get a meaningful result you need one of the points your testing to be at a known voltage like the ground bar or neutral bar which should be at 0 volts or very close to 0v.
 
Thanks for the reply.

"If the circuit has no load connected ie there's nothing plugged into it then that live wire will be 'floating'"

Is it true even when the breaker is off? I was thinking if the breaker is off, the voltage of the lower screw is zero.
 
In theory it is zero, however, there are several reasons why this voltage could be there.
type of test meter makes a difference
it would be a guess to start assuming why the voltage is being measured, some reasons are normal , other reasons are down to a fault within the installation.
 

Reply to what is the voltage? 180 volt? 220 volt - Myanmar in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
810
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
857

Similar threads

  • Question
Indeed. And always worth giving the batteries a few spins while in place - sometimes cleans the contact areas up a bit.
Replies
7
Views
640
Hi all, This may is a little odd and may take some getting your head around but here goes... I measured around half the load current on two DC...
Replies
0
Views
428

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top