I'm going to post up the worst schedule of test results you will ever see! Build it up bit by bit and discuss the things that are wrong with it. Here is the first part, 3 things wrong on it (apart form the date, thats just me messing about).


[ElectriciansForums.net] What is Wrong with this Test Sheet?

Post up what you think is incorrect and why. I'll add another part to this schedule of test results later in the week.
 
Its a 1.5mm cable protected by 32a breaker. 32a breaker will not be sufficient to protect the cable. Fire hazard.

Half way there mate. 1.5mm RFC????

Breaking capacity exceeds ipf?

Erm... no.... May need to do the calcs on this one? We have the Ze, the ipf @230V nominal Voltage. Why is it wrong on the test sheet??
 
Im confused now mate, is the IPF wrong or is it the PSCC reading? which would make the Zdb of 0.18 irrelevant to the recorded 4.7Ka. :)

Does the 1.5mm2 require OL protection or due to the nature of the connected loads is just fault protection required?
 
Ok cool, 230/0.18 = 1278A

Just wondered if maybe it was the PSCC reading as it could be higher than the 1278A PEFC. Phase sequence not applicable though so doubt it would be that high.

1.5mm2 is not suitable on a 32A (unless it was MICC perhaps)
 

Reply to What is Wrong with this Test Sheet? in the Electrical Course Trainees Only area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
957
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top