Evening all,
Was thinking the other day about an installation I've seen where the 2 earths of a ring main at the DB were covered in one sheath of sleeving.
This made me wonder whether end to end tests would have been carried out or not. Would someone do the tests and then put the sleeving on?
I know I make off a board and then carry out the testing when all cables are terminated.
Are there any other things you all come across which make you question whether things might have been missed?
I get the sleeving on asap myself, as I dislike bare copper flying around, especially if the incomer is live on the supply side or if it's a 3 phase board.
No reason why someone couldn't test and then sleeve though.
It's also theoretically possible the end to ends might have been done at a socket.
Evening all,
Sorry to be pedantic but it's a ring final circuit not a ring main.
But I do get what you're getting at. Attention to details is important in this job, and a lack thereof can lead one to question the integrity of the workmanship as a whole...
In theory you could twist all the cpcs from every single circuit together as one big twisted mess and put under just one single length of wide earth sleeve.…
the next bloke would have a wonderful time trying to work out what the heck is going on
Old habit of wanting to second fix everything including the DB before I test. Testings always last on my to do list.
Do most people test one circuit then terminate, then another and another until all are done?
Usually have all cables taped, marked and tested before the board goes on the wall.
Otherwise your wiring the board twice.
Much easier to to test as well.
I dead test before the cable gets anywhere near the new board. Once it’s dressed in the board it’s connected and that’s it. I can not get my head round doing the board then trying to test, that’s all backwards….
and....dead testing before connecting ensures you ain't got 1 leg of a RFC connected in with a radial instead of it's "correct" other leg.
@ToonSparky is correct to terminate into the board before testing, at least for the CPCs anyway. If you're not connecting the CPCs to the earthing arrangement, then your IR testing is non compliant:
643.3.1 The insulation resistance shall be measured between live conductors and between live conductors and the protective conductor connected to the earthing arrangement
GN3 (17th ed, am3) tells me that this requirement came in in 2008, prior to this you could just test to the CPC without it terminated. Old habits die hard huh?
Maybe this is why I was taught to do it this way back when I was an apprentice.
So it could be worthwhile carrying out all R1+R2 and end to end tests while disconnected from the board but IR tests onwards cables should be terminated?
Sure, no reason I can think of why you shouldn't do it that way. Much easier to find which conductor belongs to which leg of a ring final for the fig.of 8 tests if you do it before the cables are terminated
Am I being completely thick , but why? do you need to connect the earths to the earth bar to conduct your initial IR tests
at college we did dead tests prior to connecting circuits to the board
@Dustydazzler
This is done so that any cable that may have become damaged during installation is tested to earth as well. That way you can be sure there is definitely no faults through say the building steel ect that would have been missed by doing the test disconnected from the earth bar. If that makes sense
Although there is nothing to stop you IR testing circuit lives to incoming CPC, or MET if local, as well as circuit CPC to tick that box.
IR becomes a five point test (obviously not TPN) instead of three but the ease of access and not having to redress the CU makes it worth it.
Newcastle Upon Tyne
United Kingdom
What makes you question things?
IAmSparkytus!,
GBDamo,