sparky1ste

My max permitted Zs for a circuit is 0.05 - my calculated Zs = 0.07 - 240mm swa cable on 630a MCCB (adjustable)ZE at origin 0.01 (substation otherside of wall) - got this as a code 2 but no way of fixing this excessive earth loop impedence so a satisfactory report can be achieved. any thoughts! Ps. I know MCCB is oversized but when adjusted it is still over the max!
 
What does it say in the manufacturers data sheet that came with the 630A MCCB?? Why are you calculating rather than measuring. Depending on your test equipment, you may have to implement IQ's supplementary resistance method, (see Sticky's above) to obtain a realistically accurate measurement... Anyway, ....check manufacturers data first.
 
its a tough call
when the difference between pass and fail of such low values can be just 1 / 100th of an ohm , can you rely on the resolution of standard test equipment to get the right readings so close to the Tx ?
unlikely tbh.

and as you say there aint no quick & easy fix beyond adjusting the mccb.
if they really want a followed up pass remedial , downrating the mccb & thus the circuit also , may have to be considered , or improve the earth path even.
 
its a tough call
when the difference between pass and fail of such low values can be just 1 / 100th of an ohm , can you rely on the resolution of standard test equipment to get the right readings so close to the Tx ?
unlikely tbh.

and as you say there aint no quick & easy fix beyond adjusting the mccb.
if they really want a followed up pass remedial , downrating the mccb & thus the circuit also , may have to be considered , or improve the earth path even.

Yep, not many here will have a high resolution ELI tester, that's for sure!! Improving the earth path is going to be a hit and miss affair too, short of connecting a suitably sized separate CPC from the the substations MET.

Manufacturers will generally only give a max Zs figure, not a Zs value for every setting on a adjustable MCCB, which is why i advised the OP to check the data sheet first, or better still contact the manufacturers technical dept direct. Replacing the 630A MCCB for a smaller one to suit the connected load, could turn out to be an expensive exercise, so best left as a last resort.
 

Reply to the thread, titled "what next!" which is posted in Periodic Inspection Reporting & Certification on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
what next!
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
6

Thread Tags

Tags Tags
None

Advert

Thread statistics

Created
sparky1ste,
Last reply from
sparky1ste,
Replies
6
Views
1,398

Advert

Back
Top