Went to a job today full rewire to include garage conversion the person that did the job asked for payment and said he would be back in a couple of days to finish off and issue certificate and yes he hasnt been seen since (What a suprise).
Some of what I found, meter tails melted, CU 2 thirds on board the rest flapping in the wind. Two 2.5mm T&E and one 1.5 T&E not connected. 35 downlighters on the one circuit fire damage evident and when I went into attic no fire protection at all on any of them and two joists already black from the heat. I could go on but you get the idea.
Told him wont touch it needs PIR first he AGREED picked myself up of the floor now I have never had this before. Can I now issue an EIC and cross reference to PIR for the work that I do or is it something else.
Thanks
Chris
Some of what I found, meter tails melted, CU 2 thirds on board the rest flapping in the wind. Two 2.5mm T&E and one 1.5 T&E not connected. 35 downlighters on the one circuit fire damage evident and when I went into attic no fire protection at all on any of them and two joists already black from the heat. I could go on but you get the idea.