ball park figure:
The actual number is beyond my limited old brain
Insulation res. test n&e would trip (set 500v) rsbo/rcd
What is the threshold / trip ...not trip, ohms reading on tester
I guess some manufacturers may differ slightly, but there must be an inbetweeny?
In the old days, n&e faults were not so important (re-tripping breakers) cos of course no rcd's/rcbo's to worry about...
However, the 'board' would not connect a new supply with a 'low reading' Live Earth or Neutral Earth
Many times low readings were due to damp conditions, new builds. damp plaster etc. Nevertheless the board would not connect until 'their megger' said ok....
 
A 30mA RCD/RCBO could trip anywhere between 16 - 30mA so in theory anything over 14.4kΩ (230V ÷ 16mA = 14375Ω) and it shouldn't trip. The regs however require 1MΩ and anything under 2MΩ requires further investigation.
 
Last edited by a moderator:
8000 ohms ish at 30mA ?

I'd go a bit higher (Bruce Forsyth style) as a correctly functioning 30mA device will give up at around 24mA....9500ohms.

Anything below 2Mohms requires further investigation anyway.
 
Last edited by a moderator:
Eh?
How can Ohms trip an rcbo, it's not possible.
It is the current flowing that will trip a protective device NOT the resistance.
What the heck are you lot on about?
 
If you have a low enough resistance then 230 Volts will drive a current capable of tripping an rcd - somewhere between 16mA and 30mA for a common 30mA device (often about 22)
So R = 230/0.03A (or 0.022ishA)
 
Eh?
How can Ohms trip an rcbo, it's not possible.
It is the current flowing that will trip a protective device NOT the resistance.
What the heck are you lot on about?
Must admit it confused the heck out of me yesterday (I thought better of it and deleted the someone tongue in cheek post I posted). ;)
 
Well.I didn't contribute,because I just cant do the maths :26:
icon7.png
 
Depends where the resistor is placed.

7-8K should be low enough to trip an RCD if it's between Live and Earth. I'll let someone else work out how low it has to be to trip the RDC if it's between Neutral and Earth :-)
 
Try this link it maybe able to help

RCD - DIYWiki

The earth reference wire references the neutral so when an unexpected current/voltage spikes flows causes a change in voltage between the earth and neutral the RCD will trip automatically.
As you read they were initially designed to pick up failed neutral faults on pme systems faults
 
This description of how they work also worth a read...

How RCDs work (residual current device circuit breakers): Explain that stuff!

Basically the current flowing in live and neutral create oposing magnetic fields in a torroid in the RCD. If they are identical the net result is no magnetic field. If there is a missmatch the resulting magnetic field is picked up in a coil and used to operate the relay that disconnects the power.

The problem with calculating an equivalent resistance that will trip out the RCD if placed between neutral and earth comes about because the neutral point of an supply is often connected to earth.
 
This description of how they work also worth a read...

How RCDs work (residual current device circuit breakers): Explain that stuff!

Basically the current flowing in live and neutral create oposing magnetic fields in a torroid in the RCD. If they are identical the net result is no magnetic field. If there is a missmatch the resulting magnetic field is picked up in a coil and used to operate the relay that disconnects the power.

The problem with calculating an equivalent resistance that will trip out the RCD if placed between neutral and earth comes about because the neutral point of an supply is often connected to earth.

Yes, I agree, but that doesn't explain why a non-energized RCD will sometimes trip when another circuit is activated... If you see what I mean
 
is that because of voltages present on the neutral bar , therefore present on all circiuts connected to the neutral bar . even when off. ? ,,,,,

Sent from my GT-S5830 using Tapatalk
 
is that because of voltages present on the neutral bar , therefore present on all circiuts connected to the neutral bar . even when off. ? ,,,,,

Sent from my GT-S5830 using Tapatalk

Yep, its the nature of the design of some RCBOs, a sudden surge of voltage on an independent circuit where the neutrals are separated between two dbs causes a momentary unbalance between the earth and neutral.
 
Thanks guys, some interesting points
i guess some rcbo's / rcd's are more sensitive than others
A bit like people really -;
 
Yes, I agree, but that doesn't explain why a non-energized RCD will sometimes trip when another circuit is activated... If you see what I mean

In an ideal world Live and Neutral would follow exactly the same path so that any influence from another circuit would effect both equally. However that's not possible.

It's also not unknown for people to "borrow" a neutral from one circuit to use on another. That can cause the neutral current on circuit 1 not to match the live current on curcuit 1 ..and trip out the RCD.
 
In an ideal world Live and Neutral would follow exactly the same path so that any influence from another circuit would effect both equally. However that's not possible.

It's also not unknown for people to "borrow" a neutral from one circuit to use on another. That can cause the neutral current on circuit 1 not to match the live current on curcuit 1 ..and trip out the RCD.

almost garanteed on thw landing light. lol

Sent from my GT-S5830 using Tapatalk
 
ball park figure:
The actual number is beyond my limited old brain
Insulation res. test n&e would trip (set 500v) rsbo/rcd
What is the threshold / trip ...not trip, ohms reading on tester
I guess some manufacturers may differ slightly, but there must be an inbetweeny?
In the old days, n&e faults were not so important (re-tripping breakers) cos of course no rcd's/rcbo's to worry about...
However, the 'board' would not connect a new supply with a 'low reading' Live Earth or Neutral Earth
Many times low readings were due to damp conditions, new builds. damp plaster etc. Nevertheless the board would not connect until 'their megger' said ok....
The actual figure is 7666.66 ohms but that's at bang on 230 volts, if the voltage was 240 (which it's usually nearer) it would be 8000 ohms as someone else has indicated.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
what ohms trips rcbo's
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
20

Advert

Thread statistics

Created
wattsup,
Last reply from
davie spark,
Replies
20
Views
14,821

Advert

Back
Top