Hey guys, just out of interest, just completed a job for a customer but whilst i was in the board(old 5 way wylex) i noticed both ring circuits on one 32a fuse (space saving?)and cant rememeber off the top of my head and wondered if one of you lovely people knew the actual reg that states its a possible no no? i know its bad practise but just wondered if there was an actual reg?
Cheers,
lawman
 
can't think of a reg apart from the one about separation of circuits and discrimination betwixt them (sorry no regs to hand)

As a safety thing can't think of a bad point apart from premature ..... tripping. As in too many things plugged in expecting the capacity afforded by two RFC's
 
If they are both installed separately in accordance with appendix 15 and 433.1.5 then the only issue is with regard to section 314 (Division of installation).
I suspect though that it is likely that 433.1 will not be complied with as it is likely that "Ib" will possibly exceed "In" in some circumstances.
 
Ive been looking through regs and scratching my head! Thats what i thought, from a safety point of view the only bad point might be its gonna trip because they may overload it in the future? well, i pointed it out to them but they said they havent ever had any trouble so mehh!!

I like what your saying widdler 314 looks good, just found it in regs and 433.1!

cheers for your quick knowledge!
 
Last edited by a moderator:
Definition of a 'circuit' - An assembly of electrical equipment supplied from the same origin and protected against overcurrent by the same protective device(s).

Two ring finals in one MCB would be one circuit, not two circuits in one MCB. Pretty crap though.
 
Last edited by a moderator:
Definitions, rfc = a final circuit arranged in the form of a ring and connected to a single point of supply.

No mention of 2 rfc on the same point of supply. Erm good question.

Only other thing from top of my head is appendix 15, "An unfused spur may be connected to the origin of the circuit in the distribution board". It says "an" not "another ring".
 
Have a look at the first line of reg 537.2.1.1 and now member the description in definitions of a "ring final 'circuit'.

Imho a rfc is one circuit and two should not be placed on the same mcb/fuse.
 
In that case, two times two loops of cable connected together in a single MCB isn't a ring final circuit, merely two times two loops of cable in a single MCB and by definition, a circuit.

I'm not arguing a case for this cack design of a circuit, just struggling to argue against it.
 
Last edited by a moderator:
Doh, I've written a long post and lost it in cyber space. Not doing it again, its to late.

Gary I agree with you. In the end there is no reg set in stone against this but would anyone of us do it? No.

Can anybody show us a reg?
 

Reply to What Reg states you cant have 2 RFC's in one fuse? in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
311
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
834
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
940

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top