The other week i got a call from a little granny who had a leak in the loft which caused some of the lights to trip out and sockets etc.

I went there and isolated the affected circuits. I said i would go back in a week after everythings dried out and recconnect.

Any way, i though i would do a little zs on some of the sockets. Results i was getting was 2.19 ohms.

So i did a Ze test at origin and found just over 2 ohms. Checked main incomer and found there was no earth coming from the head.

We called eon and when they came round to have a look they told us that it wasnt there problem and it was up to the electrician to supply earth via earth rod.

The property is not in a rural area its on a normal street.

The board is 16th edition board, so was thinkng i would put a couple of rcbos in for lighting and sockets and stick an earth rod in.

Is this ok, would i need to put an rcd before the fuse board??
 
if you are providing a TT earthing arrangement, you need all circuits to be protected by 30mA RCD. easiest and cheapest way would be to replace main switch with RCD, but not compliant with 17th as regards splitting of circuits to minimise inconvenience.
 
if you are providing a TT earthing arrangement, you need all circuits to be protected by 30mA RCD. easiest and cheapest way would be to replace main switch with RCD, but not compliant with 17th as regards splitting of circuits to minimise inconvenience.

Do all circuits need RCD protection even if BS7671 maximum Zs readings are met?
 
In general, if the CU is plastic, and the tails are sheathed, then only the circuits fed from the CU require RCD protection.
If the CU is metal, then a stand alone RCD will be required between the meter and the CU.
You might be able to get away with using a plastic stuffing gland where the tails enter the CU.
If the tails are not sheated, then they will require changing, including any that belong to the DNO.
 
In general, if the CU is plastic, and the tails are sheathed, then only the circuits fed from the CU require RCD protection.
If the CU is metal, then a stand alone RCD will be required between the meter and the CU.
You might be able to get away with using a plastic stuffing gland where the tails enter the CU.
If the tails are not sheated, then they will require changing, including any that belong to the DNO.

Where do the regs state that?

(I am not being a pedant, I am genuinely unsure and interested!)
 
We called eon and when they came round to have a look they told us that it wasnt there problem and it was up to the electrician to supply earth via earth rod.

The property is not in a rural area its on a normal street.

Are all the other properties on the street on a TT system?

What is the main earth at the moment? If it's not coming from the DNO, presumably it's a rod, but 2 ohms is pretty unrealistic for a TT isn't it?
 
is it a terrace?..or a semi?......as 2 ohms is way too low for a TT......just wondering if theres a shared supply here and theres a secret earth someware going to next doors service head.......
 
Had a similar situation a couple of years ago. Contacted DNO and they were there within the hour. TN-C-S provided. Presumably there is evidence of an existing earth connection at origin ? If so and not TT, I would contact them again being more insistent.
 
Where do the regs state that?

(I am not being a pedant, I am genuinely unsure and interested!)
In general, there are two methods used to provide fault protection in domestic installations: ADS and double insulation.
Section 411 provides information on ADS, Section 412 provides information on double insulation.
There are other methods for providing fault protection, but they are not really practicable for dometic installlations.
With a TT installation, ADS can be provided by use of an RCD, however unless the supplier provides such a device, there will always be a part of the installation (between the cut-oyt and your RCD) which will not be protected. That part can be protected by use of double/reinforced insulation.
 

Reply to What should i do with this one? in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
285
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
787
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
804

Similar threads

  • Question
I think I might be tempted to test this theory, if it can be done without causing danger to anyone.
Replies
11
Views
2K
N
  • Article
Found a plumbing course but not what I expected? Hi all, I posted a question back in 2020 so rather than bringing that thread back up thought...
Replies
0
Views
336
newbie123
N

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top