Ramjam
I have been installing 2.5mm T&E from loft mounted inverter to consumer unit. Cable protected by 16amp MCB
Have you seen page 140 of the regs where it has the formula Iz Greater than or equal to In + Ig where Iz is the current carrying capacity of the conductor and Ib is the MCB rating and Ig is the inverter output?
By that formula we should be using a 4, 6 or 10mm cable depending upon the fixing method.
I can't see the reason for this and I don't think this is common practice, is this just one of those regulations that get ignored???
Perhaps this can be explained away by someone more conversant with BS7671?