what size armoured cable | on ElectriciansForums
Discuss what size armoured cable in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
L
leeweimaraner
i need to run a supply to a garage 90metres from the fuse board the garage will have electric door ,sockets and lights ,may want to run a hot tub from the garage?? what size armoured cable should i use and why???
You first of all need to know how many amps the cable is drawing and then work out the voltage drop to come up with the correct size.
The hot tub...5kw?
Garage door 2kw?
Sockets & lighting 4kw +?
90M!
25mm 3-core swa on a 63 amp breaker
(assuming single phase)
Maximum Demand with applied diversity (my calculations)
Garage supply
Lighting: ? type plus watts
Hot tub:
100% 5kW/230 = 21A
Power
1 x ring main @ 100% = 30A
1 x radial (garage door) 2kW/230 = 9A
Estimated total amount of power of 50A
Phase: Single Phase
Power:11.5 kilowatts / 50 amps
Length:90m
Core Size: 25 mm²
Voltage Drop:8.55 volts
As diversity isn't and exact science I'd ask yourself if you'd use the hot tub whilst using the sockets and garage door.
That might lower the design current with regards to power hence small cable size.
ok you are saying 11kw how do yuo get to 25mm cable please
Ib = 11000/230 = 48A
select In as : Ib < In (say 50A mcb allowing some diversity)
calculate max mV/A/m
max volt drop x 1000 = 2.66
Ib x length
select suitable cable for volt drop from table 4E4A (25mm closest)
determine It value (116A)
calculate Iz (It x Ca x Cg x Ct)
in this case i assume) Iz = It = 116A
Iz must be bigger than In = true
therefore 25mm is the smallest size of cable that satisfies both volt drop and current carrying requirements
The VD is Irrelevant here! The cable is still 25mm. If you look back to my original reply you'll see a question mark with regards to lighting which when calculating diversity is relevant.
ezzkiel says "Whoopee do Marc your amazing! let me suck your lolly pop"!
I was merely pointing out that the value was above the max permitted which to me IS relavent.
Well thank you Marc!
Is it lighting or power? Well has the power and the lighting are a complete factor in terms of design current, I'll choose the lowest VD percent in Lenny's case lighting. That's odd the cable size is still 25mm.
My VD for a 70degreeC 25mm PVC SWA with a 50A Ib at 90M comes out to 7.87V.
Worst case scenario obviously, not likely to pull 50A all the time.
I was factoring in diversity there, but if the 11kw is a constant load then yes it's the lower limit
  • [ElectriciansForums.net] what size armoured cable
Reply to what size armoured cable in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
I assume said contractor is part of a Part P scheme (NICEIC, Napit, few others..) in which case complain to them. They'll investigate (in theory)...