Just checking the regs for size of circuit breaker or rcbo to protect pv. the regs only says Type B as far as I can see:shades_smile:
 
Just had a look through the paper work nothing immediately apparent it does say on the side of the invertor which is a Stecca 500, 5 Amp Max does that mean I can use 6 Amp RCBO:bow:
 
Just had a look through the paper work nothing immediately apparent it does say on the side of the invertor which is a Stecca 500, 5 Amp Max does that mean I can use 6 Amp RCBO:bow:

In terms of circuit breaker size that is fine by the look of it

Whether a rcbo is right is another issue. The inverter is transformerless, so unless the manufacturer makes the appropriate declaration then if you are including the residual current protection as part of ADS (ie TT or large Zs) then it must be a Type B rcd (712.411.3.2.1.1). The standard rcbo will not be. As long as you do not have buried cables you might be better off without a rcd/rcbo. I could not see anything in the datasheets about likely leakage.

Regards
Bruce
 

Reply to What size circuit breaker or rcbo in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
361
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
920
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Given the apparent lack of earth, combined with no short circuit or over current protection, I'd contend that luck has been the sole factor...
Replies
5
Views
601
nicebutdim
N
Sort of; technically speaking the 10mA is required to hit the 40mS target at 50-149mA, whereas the 30mA device can be happily snoozing along for...
Replies
8
Views
803

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top