A relative in West Cheshire sent me this pic. He is contemplating having an EV charger and other electrical appliances fitted. He asked me if he has a 60A or 100A supply. From this pic, it looks like a 100A supply with 60A fuse fitted for some reason. He wants it to be 100A. Any ideas?

[ElectriciansForums.net] What size is this supply?




[ElectriciansForums.net] What size is this supply?
 
It doesn't matter if the incoming cable is capable of 100A, it still doesn't mean that supply has a capacity of 100A.

DNOs apply diversity just as electricians do, the capacity of the distribution transformer determines how many supplies may be connected at 60A, upping some customers to 100A may well mean a larger transformer is required.

One cannot assume that because a certain size cable, fuse carrier, meter etc has been fitted that there is capacity.

I doubt the fuse has been changed, the meter fitter is likely to have removed the fuse, fitted meter, refited the fuse, applied new seals, and applied a label showing the fuse size.
Something tells me he was downgraded - just a hunch. If he was dowgarded to a 60A fuse, which does happen, you will find the DNO would have marked out streets or an area then put 60A in the lot. Or ensured 60A was inserted when a smart meter was fitted, as take up may be enough to make a difference in downgrading in an area. They do it by stealth. This maybe in preparartion for the EV charger onslaught, followed by elimination of gas. Hopefully in the interim they put in enough electrical capacity.

An all electric house they would have left alone, as the odd 100A draw off makes no difference here or there. Few houses with gas supplies are all electric. Especially those built with heating systems from new.

He needs to look in houses around to see if they still have 100A supplies. All those adjacent foolishly took up the big brother smart meter, so they all may have 60A fuses.
 
I had the DNO out once to pull a old fuse, tails were 16mm between cutout and meter, from meter to CU 25mm, it had a 100A fuse, due to tails being 16mm he said he would have to down rate to 80 or 60. I said no thanks wait there and got some 25mm off the van, then changed the tails and said we will keep the 100A if you dont mind, he phoned the depot and begrudgingly put it back in... i thought it was a matter of principle
 
I’ve never known of a smart meter installer change a fuse rating, ever. I don’t think they are allowed to.
In fact they have a form for if the tails are undersized and tell the customer to contact a sparks. I’ve seen this a few times. In my area they kindly fit 25mm tails to an isolator too.

It seems rather pointless speculating about what might have been the case once, and which bunch of capitalists are to blame, the bottom line is it has a 60amp supply and if he really needs more then he needs to phone the DNO.
 
I’ve never known of a smart meter installer change a fuse rating, ever. I don’t think they are allowed to.
In fact they have a form for if the tails are undersized and tell the customer to contact a sparks. I’ve seen this a few times. In my area they kindly fit 25mm tails to an isolator too.

It seems rather pointless speculating about what might have been the case once, and which bunch of capitalists are to blame, the bottom line is it has a 60amp supply and if he really needs more then he needs to phone the DNO.
I can only speak as a former energy provider MOP, we were not allowed to down grade or up grade cutout fuses, cant speak for other providers.
 
I had the DNO out once to pull a old fuse, tails were 16mm between cutout and meter, from meter to CU 25mm, it had a 100A fuse, due to tails being 16mm he said he would have to down rate to 80 or 60. I said no thanks wait there and got some 25mm off the van, then changed the tails and said we will keep the 100A if you dont mind, he phoned the depot and begrudgingly put it back in... i thought it was a matter of principle
I have the impression they told him to downgrade whenever he could. It would be fun if hubby had high current drawing equipment in his rear workshop the DNO man never knew about.

Why did he make a phone call to the depot? That makes no sese. Maybe he was told to drop the rating before going - a matter of policy.
 

Reply to What size is this supply? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
951
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

When he bought the bank, they stripped out all the metalwork, iron bars etc for scrap. He was left with the cashier countertops… which have been...
Replies
2
Views
441
  • Question
Nothing wrong with it. Which manufacturers have you got this information from? What do you mean by trip speed? Fuses and MCBs can operate in the...
Replies
11
Views
2K
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top