Further to my last post, I'm trying to work out what MCB I should be buying for my instantaneous water heater.
I have a Hyco which is rated at 12.8kW. It has 3 metres of 10mm cable running to it from the CU - 1.5m is clipped to the wall of the airing cupboard, the other 1.5m runs in 3" trunking which it shares with the central heating boiler (9kW), but they won't be on at the same time.
I did the voltage drop calcs, using ambient temperature of 25degrees, voltage at 240v (measured) and the numbers came out at
Cable Size 10mm
Voltage Drop 0.704v
Percentage Drop 0.29%
Current Load 53.3amps
Max Cable Load 65.9amps
Whilst I understand the MCB is there to protect the cable from overloading and overheating, I also understood that the MCB had to be rated in excess of the anticipated demand. My problem is, I can't find a 55amp or 60amp MCB for my MK Sentry.
The MCB currently protecting the circuit is only 45amps. I would have thought it would have tripped as soon as the heater came on, but to date it hasn't at all. Is it most likely that although the heater is rated at 12.8kW, it's using less or might there be some other reason (I'd really like to put a clamp meter on and see what it's actually drawing - I guess I'll just have to invest the £50 or so and get one)!
Thanks guys
stu
Further to my last post, I'm trying to work out what MCB I should be buying for my instantaneous water heater.
I have a Hyco which is rated at 12.8kW. It has 3 metres of 10mm cable running to it from the CU - 1.5m is clipped to the wall of the airing cupboard, the other 1.5m runs in 3" trunking which it shares with the central heating boiler (9kW), but they won't be on at the same time.
I did the voltage drop calcs, using ambient temperature of 25degrees, voltage at 240v (measured) and the numbers came out at
Cable Size 10mm
Voltage Drop 0.704v
Percentage Drop 0.29%
Current Load 53.3amps
Max Cable Load 65.9amps
Whilst I understand the MCB is there to protect the cable from overloading and overheating, I also understood that the MCB had to be rated in excess of the anticipated demand. My problem is, I can't find a 55amp or 60amp MCB for my MK Sentry.
The MCB currently protecting the circuit is only 45amps. I would have thought it would have tripped as soon as the heater came on, but to date it hasn't at all. Is it most likely that although the heater is rated at 12.8kW, it's using less or might there be some other reason (I'd really like to put a clamp meter on and see what it's actually drawing - I guess I'll just have to invest the £50 or so and get one)!