So here's the info straight from a DNO:
[FONT="]"Calculation of the size of the SSEG[/FONT][FONT="]
[/FONT]
· [FONT="]Add the total rating of all of the solar panels. Call this SP_Rating.[/FONT]
· [FONT="]Identify the efficiency of the inverter. Some inverters have charts showing how the efficiency varies with the DC Input Voltage, and other factors, and some just state an 'Average Efficiency'. Call this Inverter_Efficiency.[/FONT]
· [FONT="]Multiply the two figures (i.e. SP_Rating x Inverter_Efficiency). Call this Output_1.[/FONT]
· [FONT="]Compare Output_1 with the maximum rated output of the Inverter. Take the smaller figure. This is the SSEG output which should be reported.[/FONT]
[FONT="]
[/FONT]
[FONT="]Consider the following worked example:[/FONT]
[FONT="]7 solar panels rated at 235 Watts each, with a Sunny Boy 1200, (rated at 1200 Watts)[/FONT]
[FONT="]
[/FONT]
[FONT="]7 x 235 = 1645 Watts (SP_Rating)[/FONT]
[FONT="]
[/FONT]
[FONT="]Inverter Efficiency = 92% (Inverter_Efficiency).[/FONT]
[FONT="]
[/FONT]
[FONT="]SP_Rating x Inverter_Efficiency = Output_1.[/FONT]
[FONT="]
[/FONT]
[FONT="]1645 x 92% = 1513.4 Watts (Output_1)[/FONT]
[FONT="]
Compare Output_1 (1513.4 Watts) with the rated output of the Sunny Boy 1200 (1200 Watts), and take the smaller figure, which is 1200 Watts
[/FONT][FONT="]If you are considering an installation which is between 3.68 and 4kW, then you will need to Apply for permission to connect this generation[/FONT][FONT="]"
So that final figure is what they are saying should not go above 3.68kW. I guess we can work backwards from that to suss out the largest array possible for a given efficiency of inverter.