Im going to do a dead test an installation that has a kitchen ring with 5 different loads on a grid switch. If possible i would like advice with regards to my approach to testing this circuit. What i would do is as follows for continuity:
1) End to end L-L, N-N, Cpc-Cpc,
2 Cross connect Incoming L- outgoing Cpc, than test at each socket for the sake of any bridges or rings within ring as well as documenting R1 + R2 of the ring. Now the loads off the grid switch i.e the cables should be tested to make sure of correct polarity as well as cables are connected securely and are in good order too. Should any readings with regards to these (spur type loads off of the grid switch be recorded?) or just noted.
I know to leave the switches on when carrying out the IR test and will initially soft test at 250v as there are neons which are known to affect test results, if all is ok i will join L-N and test to earth at 500v.
Is there anything that i may have missed or any advice that may simplify but appropriately help with regards to my approach, or is there anything i have missed out?.
Sorry if this sounds like basic stuff i just need clarification with regards to this test as never had to test with grid switch situation.
many thanks
Greeny!!!
1) End to end L-L, N-N, Cpc-Cpc,
2 Cross connect Incoming L- outgoing Cpc, than test at each socket for the sake of any bridges or rings within ring as well as documenting R1 + R2 of the ring. Now the loads off the grid switch i.e the cables should be tested to make sure of correct polarity as well as cables are connected securely and are in good order too. Should any readings with regards to these (spur type loads off of the grid switch be recorded?) or just noted.
I know to leave the switches on when carrying out the IR test and will initially soft test at 250v as there are neons which are known to affect test results, if all is ok i will join L-N and test to earth at 500v.
Is there anything that i may have missed or any advice that may simplify but appropriately help with regards to my approach, or is there anything i have missed out?.
Sorry if this sounds like basic stuff i just need clarification with regards to this test as never had to test with grid switch situation.
many thanks
Greeny!!!