What type is this RCD? | on ElectriciansForums
Discuss What type is this RCD? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Goody
London
What do I put down on the EIC on “Type BS EN” field for an RCD WRS80/2, is it Type AC? Thanks!
The BS EN will be 61008 and the type will be AC.
They types are -
A = Protection against AC earth fault currents containing pulsating DC components
B = Protection against DC earth fault currents
AC = Protection against AC earth fault currents
S = Delayed
Where is this field? Do you mean on the schedule of test results? If so, the BS EN field is for overcurrent device, not RCD!
If being used as a main switch, then just put down BSEN 61008-1. The RCD "type" is irrelevant, just put a dash!
There is also an RCD section on the SOTR, well there is on the BS 7671-2008 example forms.
Reply to What type is this RCD? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Your drawing suggests that you might be modifying the DB beyond the manufacturer's design specification. If so, this could see you in breach of...
Thanks Westward, and that last paragraph with the Note about no characteristic marking is exactly what I needed to see.