What value | on ElectriciansForums
Discuss What value in the UK Electrical Forum area at ElectriciansForums.net
Farmelectrics
Wirral
Ok so we no that for are insulation resistance tests 1 M ohm is the acceptable value well greater than that is but how do work out say for a 6 amp b type breaker how low would your reading have to go before it takes the breaker out
I'm a bit confused by the question, a 6A B-Curve breaker isn't a very good detector of leakage current from an IR fault.
R=V/I so to achieve 6A of leakage your insulation value would need to be 38.3ohms (38million M ohms)
Murdoch if you have a short it will show zero on your tester if your insulation is poor or damaged it might show for example 0.4M ohm which is not acceptable but how low would the reading need to go to disconnect your protective device
Reply to What value in the UK Electrical Forum area at ElectriciansForums.net
Yes I touched on diverted neutrals when I went over guidance note 3 the first time but I’m doing a second round and going between all books whilst...