Have had bit of a nightmare with a job of installing a replacement 15KW extraction system motor in a workshop.
The previous motor was just DOL so only one 3 core cable between the workshop and the motor which is outside, the otherside of building.
The new extraction system came with star-delta starter.
The customer needed this done ASAP and being very busy i agreed to wire the motor in delta and connect to main contactor in star-delta starter (knowing there would be a 10sec lag). Already 50A type D mcb which seemed sufficiant to me?
With the intention of replacing the cable with a 7 core when have a bit more time.
However when starting, it would trip the MCB, which had me slightly puzzled, as whilst the start up current will be high a 50A D should have covered this.
So spoke with the manufacturers technical department, who basically said, why is it in Delta it should be wired in star-delta!
And thats about all he could tell me.
So spent yesterday afternoon fitting a whole new cable, all wired up correctly in star-delta .
Press the start button, Thump.
At this point im smashing my head on a wall.
I had only tested the wiring up to the motor to this point, so did a IR test on the motor, to my discovery there was a short on the L1 coil to earth. Ohm meter showing 0.07 ohms on both sides of the coil to earth.
L2 and L3 coil was good with no short.
So really kicking myself for not testing this brand new “tested” motor to start with!!!
So now need to speak to manufacturer again, however im worried they may claim i damaged the motor by not wiring to their reccomended specification.
Im no expert with motors etc, however i cant see how i could have caused an earth short by starting up in delta?
So what would/could cause an earth to coil short in a motor?
The previous motor was just DOL so only one 3 core cable between the workshop and the motor which is outside, the otherside of building.
The new extraction system came with star-delta starter.
The customer needed this done ASAP and being very busy i agreed to wire the motor in delta and connect to main contactor in star-delta starter (knowing there would be a 10sec lag). Already 50A type D mcb which seemed sufficiant to me?
With the intention of replacing the cable with a 7 core when have a bit more time.
However when starting, it would trip the MCB, which had me slightly puzzled, as whilst the start up current will be high a 50A D should have covered this.
So spoke with the manufacturers technical department, who basically said, why is it in Delta it should be wired in star-delta!
And thats about all he could tell me.
So spent yesterday afternoon fitting a whole new cable, all wired up correctly in star-delta .
Press the start button, Thump.
At this point im smashing my head on a wall.
I had only tested the wiring up to the motor to this point, so did a IR test on the motor, to my discovery there was a short on the L1 coil to earth. Ohm meter showing 0.07 ohms on both sides of the coil to earth.
L2 and L3 coil was good with no short.
So really kicking myself for not testing this brand new “tested” motor to start with!!!
So now need to speak to manufacturer again, however im worried they may claim i damaged the motor by not wiring to their reccomended specification.
Im no expert with motors etc, however i cant see how i could have caused an earth short by starting up in delta?
So what would/could cause an earth to coil short in a motor?