Something I haven't come across before and now its bugging me. Here is the situation.
3 phase type C mcb protecting an air con unit. The area gets a blackout for 30 mins or so, when the DNO restore power the mcb didn't trip but when tested no current was going through any of the phases on the mcb but continuity from busbar lug to the wire nut connector is present?
I took off the mcb and tested for continuity and it was fine. Replaced it back on the board and now it works? Is there something I'm missing here or something I'm not thinking of? It's strange fixing a fault when you don't know what the fault was.