Evening all.
I have just finised an EICR on a new extension. The previous electrician cannot be contacted.
The work was pretty shoddy. No identification sleeving on cables where needed including some earths. The 3 possible codes are as follows:
1. 1mm line conductor in the 6A MCB was loose due to being in with a 1.5mm and also 2.5mm conductor. I have made sure the termination is now tight but I really dont like the thought of 3 differing size conductors in the same MCB. I never do this as it is likely the smallest one will at some point not be well terminated. ?C2
2. Single socket for the fridge hidden in cupboard next to fridge, which is fine, however it is attached to the really flimsy wobbly bit of board on the back of the units. (You know the stuff, more like cardboard than wood). It is already loose. ?C2
3. Integrated LED downlights completely covered in insulation. Im not sure about this one. Its shoddy, but as they are integrated the lamp cannot be changed for a halogen so perhaps a C3 or no code? It would be a C2 if not integrated.
Cheers all.
I have just finised an EICR on a new extension. The previous electrician cannot be contacted.
The work was pretty shoddy. No identification sleeving on cables where needed including some earths. The 3 possible codes are as follows:
1. 1mm line conductor in the 6A MCB was loose due to being in with a 1.5mm and also 2.5mm conductor. I have made sure the termination is now tight but I really dont like the thought of 3 differing size conductors in the same MCB. I never do this as it is likely the smallest one will at some point not be well terminated. ?C2
2. Single socket for the fridge hidden in cupboard next to fridge, which is fine, however it is attached to the really flimsy wobbly bit of board on the back of the units. (You know the stuff, more like cardboard than wood). It is already loose. ?C2
3. Integrated LED downlights completely covered in insulation. Im not sure about this one. Its shoddy, but as they are integrated the lamp cannot be changed for a halogen so perhaps a C3 or no code? It would be a C2 if not integrated.
Cheers all.