Recently visited a new build to do a very minor job and spotted a few dodgy looking items so Client asked me to do an EICR.
Following items I found were;
Upstairs and downstairs smoke detectors mains fed but not interlinked, on separate circuits.
downlights open backed and clearly not fire rated, covered in insulation despite label stating they shouldn't be.
no lighting back boxes earthed. (so full of cables, any of which coming into contact with box would liven it up "floating" including the 2 fixing screws
Structural steel not bonded.
Single insulated cables hanging loose on approx. 2 meter run, at chest height
Main tails from meter into enclosure stuck in 50amp connectors with SWA feeding ccu 10 meters away with no switchfuse
I reported these among a few others and gave them all c2's.
This was not a pleasant experience as going behind someone and picking holes in their work is never a nice thing to do however I felt it was bad enough that it ought to be sorted out.
The original installer reacted to my report saying that I was essentially making a mountain out of a molehill and that the install was fine and had been signed off by NICEIC who had inspected it themselves as part of his yearly check up, even stating that the steel need not be bonded, as it was 'earthed' because it was stuck in the ground. So clearly not really getting the need for bonding.
This is a development of over 20 houses built in 2020.
The client has had my advice, and i have now left it with them and the original installer to sort out.
I was wondering, does anyone disagree with my above assessment of these 'c2' items
Following items I found were;
Upstairs and downstairs smoke detectors mains fed but not interlinked, on separate circuits.
downlights open backed and clearly not fire rated, covered in insulation despite label stating they shouldn't be.
no lighting back boxes earthed. (so full of cables, any of which coming into contact with box would liven it up "floating" including the 2 fixing screws
Structural steel not bonded.
Single insulated cables hanging loose on approx. 2 meter run, at chest height
Main tails from meter into enclosure stuck in 50amp connectors with SWA feeding ccu 10 meters away with no switchfuse
I reported these among a few others and gave them all c2's.
This was not a pleasant experience as going behind someone and picking holes in their work is never a nice thing to do however I felt it was bad enough that it ought to be sorted out.
The original installer reacted to my report saying that I was essentially making a mountain out of a molehill and that the install was fine and had been signed off by NICEIC who had inspected it themselves as part of his yearly check up, even stating that the steel need not be bonded, as it was 'earthed' because it was stuck in the ground. So clearly not really getting the need for bonding.
This is a development of over 20 houses built in 2020.
The client has had my advice, and i have now left it with them and the original installer to sort out.
I was wondering, does anyone disagree with my above assessment of these 'c2' items