What would you code this as. | on ElectriciansForums

Discuss What would you code this as. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Joined
Jan 30, 2021
Messages
491
Reaction score
1,449
Location
Shropshire
Doing an inspection and came across this.

Feeds are as follows:

Cutout to Meter - 25mm
Meter to connector blocks - 25mm
Connector blocks to CU’s (2 in the house) 16mm.

So far so good as the cutout is 80A not the 100A it’s labelled as.

My query is the 6mm 3 core XPLE that’s going to an outbuilding.

At the outbuilding end is 2 way CU with a 40 RCD switch and a 16a socket & 6a light circuit.

Now I know the RCD will stop the cable ever pulling more than 40A. But as it’s wired into those connectors it has the potential to pull 80a (in theory).

I’ve coded it as a C2 as to me it’s potentially dangerous given there’s no OCPD protecting the cable from the connector until it reaches the RCD in CU in the outbuilding. It’s been there approx 8yrs according to the owner and there are no signs of thermal issues anywhere at either end. But thought I’d garner opinion from the more experienced/knowledgeable folk on here.

What would you code it as? Or would you deem it safe given the RCD at the other end?

[ElectriciansForums.net] What would you code this as.
 
RCDs don't provide overcurrent protection. There is also exposed single insulation. There is no way this type of installation could be deemed safe. If there were sheathed tails feeding a switchfuse mounted by the meter fitted with suitable overcurrent protection for the distribution circuit, which then fed the (properly glanded SWA) that would be fine.
 
Gotta love it when someone asks about one issue, and the photograph they supply shows a number of others.

Apart from what was mentioned about an rcd not being an over current protection device….. how do you know that the fuse in the cutout is only 80A without pulling it?
 
Think my concern is in the Ops post and asking the question to start
Is the Op actually a electrician ?
If he is then he certainly shouldn’t be undertaking test and inspection.
Sorry @Raptor0014 but you’ve a huge hole in your knowledge.
 
Agreed the conductors of the armoured look even smallerthan the meter tails ..... Yes C2
And cable not supported, nor properly glanded, armour not earthed. Single insulated conductors not in an enclosure…

So many sins in one photo. Love to see the other end of the SWA.
 
I understand the difference between MCB's and RCD's and what they are supposed to do, but this has raised a question for me.

If RCD's only detect earth leakage what is the amp rating for? If you've got a 40a RCD and for argument's sake no MCB's and just connected something pulling 50a on the load side of the RCD, what would happen?
 
If RCD's only detect earth leakage what is the amp rating for? If you've got a 40a RCD and for argument's sake no MCB's and just connected something pulling 50a on the load side of the RCD, what would happen?
The 40A is thd maximum current that the RCD contacts have been tested to handle reliably. If you put 50amps through it then the contacts could burn out or (worse) weld together. Then the supply will not cut should an earth fault trips the RCD.
The circuit needs current limiting at the source to protect the cable itself and anything else downstream.
 
I'm also very confused by the thread.

Why would you C2 a circuit for having the potential to pull higher amperage? Wouldn't we then just condemn every installation with 100a cutout since the lights and sockets the tails feed are wired in 1.5 and 2.5mm and so could 'potentially pull 100a'?

Lost.
 

Reply to What would you code this as. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
953
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top