lawesy

Hi lads and of course the possible lasses.

I have a customer who has just had a PIR carried out, the customer has asked me if i think a new consumer unit is req. Now, they have a cons unit with MCb's and a mains isolator with a stand alone 100mA RCD to the side, I think its a expensive job to replace the cons unit as its only about 5 yrs old and in good nik. Would you replace the cons unit or just replace the 100mA RCD for a 30mA rcd to give the whole board maximun protection.

Beats me:cool:
 
is he having any work done to the installation?if so you will need to comply with 17th ed and putting the whole board on one 30mA rcd doesnt comply does it.as it has a 100mA rcd is it a tt?
 
Just change the mcb's controlling the sockets to RCBO's that would give the protection required to the 17th and you can retain the 100ma. The discrimination between the two units would mean that the 30ma would trip before the 100 so no problems with the whole installation being disconnected due to an appliance fault.

BillR3
 
ye it is a TT but it doesn't matter under the new regs PME TNS they all have the same config for the board under the 17th ed. Thing is, would you pay ÂŁ200+ for a new cons unit the one he has got now is 5yrs old, when you could have a new 30mA RCD fitted which would do the same job? Having said that, i have found a reg 531.4 handy though, this has helped.
 
I havent done my 17th yet but is not having an RCD on everything a Cat1 now?I usually work to the "Dont leave the installation any worse than found" rule.
 

Reply to What would you do? in the Talk Electrician area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
252
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
724
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
696

Similar threads

Yes the first bit is just standard wiring, TNS lead cable into cut-out, cut-out to meter, meter to DP isolator, top of isolator is sealed as per...
Replies
8
Views
1K
  • Question
Many thanks all. Very helpful to be able to bounce these things around. Was fairly happy with it all initially, but once the seed of doubt is...
Replies
8
Views
820

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top