C

cagedanimal2010

hey,
so you go to a job to add a socket, i always try and extend the ring main as appose to a 4mm spur, so i start by doing so and find out that the 2.5 t&e has a 1mm cpc, so i do the work and note on the certificate that ring main has 1 mm cpc. is this correct, or should i be suggesting to the customer that the ring main is upgraded to new cabling?
cheers guys
 
I believe it depends upon the type of protection the circuit has. If it is protected by a 3036 fuse wire then i think that it should be changed for an mcb. Don`t know the exact ins and outs of it. This is just what i have seen on other posts
 
I would extend the ring and note on the cert that the existing CPC does not meet current regulations....(assuming R1R2 and Zs and ring continuity were ok of course)....and that I dont consider it compromises the safety of the installation.
Regardless of the rights and wrongs and recommendtions ,1.0mm cpc's were and still are used without problems ,and in 30 yrs in the job I've yet to see a problem I can attribute to a 1.0mm cpc on a ring......If on a PIR I would code 4.
 

Reply to what would you do? in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
190
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

Yes the first bit is just standard wiring, TNS lead cable into cut-out, cut-out to meter, meter to DP isolator, top of isolator is sealed as per...
Replies
8
Views
1K
  • Question
Most manufacturers recommend them to be fitted. We are required to take that into account. If they had been fitted clearly it would have been...
2
Replies
27
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top