Testing a premises and all the older installation has its earthing only through the metal conduit / trunking.
I get good results on both the r1+r2 and the Zs results, but as there is no actual CPC what do I put on the report?
Thanks for your advice.
 
Just note the conduit is used as the circuit protective conductor on the cert not alot else you can do , as long as the conduit is in a good condition and not broken , it only becomes a problem if its added to or altered especially if its done in plastic
 
Testing a premises and all the older installation has its earthing only through the metal conduit / trunking.
I get good results on both the r1+r2 and the Zs results, but as there is no actual CPC what do I put on the report?
Thanks for your advice.

I'm hoping that you just mean how do you show the trunking or conduit as a CPC on your schedule rather than not knowing if it complies or not.

Just enter 'Trun' or 'Con' in the CPC box on the schedule of test results.
 
AMTEK ahen you put cable sizes on the CPC it has ARM,CON,Trunk,MICC and then a popup with sizes in mm for what ever size you put in
 

Reply to What would you put on report? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
301
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
813
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
869

Similar threads

The actual listed observations seem easily resolvable, comfortably less than a day's work. The picture of the supply poses a few questions...
Replies
5
Views
1K
  • Question
As previously posted, almost certainly due to differences in readings obtsined with high and low current measurements on the meter, low current...
Replies
10
Views
2K
OLDBOY
O

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top