Dave 85

Did a job today where I had a 6mm T&E on a 32amp retrofit MCB (re used old circuit) going into a RCD spur (13amp) then a 2.5mm going off to a shower pump. There is also an unswitched 3amp fused spur halfway down the 2.5mm with a 1mm going to a mirror light.

Sounds a bit of a muddle I know but was the only way I could do it. 3036 Fuseboard full and hard to get cable into, existing lighting circuit impossible to extend as it was buried in concrete ceiling.

My question is, on the cert, in the overcurrent protection box do I state the 32amp 60898, 13 amp 1361 or 3 amp 1361. And in the cable box do I put the 6mm, 2.5mm or 1mm.
Im guessing I'd mark it down as a 32 amp 6mm circuit as the other bits are essentially fused spurs but just wondered if anyone thought different.
 
No , your right - 6mm & 32A mcb.
The 32a mcb only protects the 6mm , spurs protect the 2.5 & 1.0
The device you record on the cert is always the one in the CU.
 
Last edited by a moderator:
Just to start a debate, surely the ocpd device protecting the point of utilisation would be the 1361's, so 2 minor works? otherwise the cert details won't make sense.
 
Just to start a debate, surely the ocpd device protecting the point of utilisation would be the 1361's, so 2 minor works? otherwise the cert details won't make sense.

Thats actually not a bad question.

Its because the MWC and EIC ask for the CU device to be recorded , at the beginning of the circuit , not any local protection downstream.
 
It's an interesting question. I would say that, for the purposes of assessing whether the Zs is suitable for the overcurrent protective device, a fused spur is actually a separate circuit.

The definition of "Circuit" in BS7671 is: An assembly of electrical equipment supplied from the same origin and protected against overcurrent by the same protective device(s). Clearly, for example, a 1mm² lighting spur supplied from a 2.5mm² ring via a FCU isn't relying on the 32A MCB in the board as its OPD; it is the BS1362 3A fuse in the FCU.

To test and certify the job properly, you may need to show separate test results for both the fused spur and the circuit it is fed from. The minor works form (in BS7671) doesn't refer to a DB, only "Protective device for the modified circuit", which could reasonably be a BS1362 fuse. The "generic schedule of test results" does refer to "Zs at DB", but maybe they didn't have enough space to add "or other circuit origin". As I think someone else said, think of the FCU as a one way DB. Clearly the schedule is laid out to cover the general case rather than the particular one of a FCU as the circuit origin, but that shouldn't stop us thinking it through properly.

In practice, I guess most of us just test and certify short spurs as part of the main circuit, but there are some cases where it makes sense to do them separately.
 
I see where you're coming from Malcolm, but an overcurrent may be an overload current or a fault current (note at the bottom of 430.3). Of course, Zs is about how quickly an earth fault current will cause the OPD to open.
 
It's an interesting question. I would say that, for the purposes of assessing whether the Zs is suitable for the overcurrent protective device, a fused spur is actually a separate circuit.

The definition of "Circuit" in BS7671 is: An assembly of electrical equipment supplied from the same origin and protected against overcurrent by the same protective device(s). Clearly, for example, a 1mm² lighting spur supplied from a 2.5mm² ring via a FCU isn't relying on the 32A MCB in the board as its OPD; it is the BS1362 3A fuse in the FCU.

To test and certify the job properly, you may need to show separate test results for both the fused spur and the circuit it is fed from. The minor works form (in BS7671) doesn't refer to a DB, only "Protective device for the modified circuit", which could reasonably be a BS1362 fuse. Thats a big leap in interpretation you must admit. Putting details on the cert of only the spur means there is no indication of which CU circuit was worked on.

The "generic schedule of test results" does refer to "Zs at DB", but maybe they didn't have enough space to add "or other circuit origin". They dont need to , the CU is the origin of any final circuit.


As I think someone else said, think of the FCU as a one way DB. No its not , they have completely different BS numbers that will be referenced in the regs under definitions.

Clearly the schedule is laid out to cover the general case rather than the particular one of a FCU as the circuit origin, but that shouldn't stop us thinking it through properly.

In practice, I guess most of us just test and certify short spurs as part of the main circuit, but there are some cases where it makes sense to do them separately.


Some good points raised though.
But to follow your example to its conclusion , your implying that the cable from the CU to the spur is a sub-mains if the spur is a DB , and the standard circuit arrangements shown in the regs do not back this up.
 
Some good points raised though.
But to follow your example to its conclusion , your implying that the cable from the CU to the spur is a sub-mains if the spur is a DB , and the standard circuit arrangements shown in the regs do not back this up.

Not a "sub-main" as such, just that it's possible to have a circuit supplied by another circuit, even if you'd describe both as "final circuits"!

I think that the people who write the regs tend to think about "standard" arrangements rather than the more untidy reality that we deal with every day.
 

Reply to What would you put on the cert? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
288
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
790
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
811

Similar threads

  • Question
😄 It wasn't the worst I seen over the weekend. Took the kids to Cumbria zoo whilst over there, and the toilets by the giraffes just had twin...
Replies
7
Views
955
  • Question
In the current book (18th, amendment 2) it is under regs 433.2 and 434.2 In most domestic situations the usual approach is the whole circuit is...
Replies
3
Views
658

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top