It is better than what most builders do which is to trim off half the cores so it fits@Dustydazzler
It's funny I nearly suggested that option above but didn't know how it would go down on here so kept quiet, I have been known to do that in the past, don't really see anything wrong with it personally!
It suggests the conductor is oversized to enable suitable termination as per manufacturer recommendations. You have also divided the conductor into separate unequal csas.@Dustydazzler
It's funny I nearly suggested that option above but didn't know how it would go down on here so kept quiet, I have been known to do that in the past, don't really see anything wrong with it personally!
How would it be half. Assuming this is a seven strand conductor the split is 43% and 57% so not half which effectively results in parallel conductors of differing csa.It is nor uncommon to just put half the cores in 1 terminal and the other half in the next terminal (assuming you have a spare terminal that is)
If not as above buy a finger lug crimp thingy
10mm or 10m it makes little difference in essence. BS7671 states parallel conductors shall be of the same csa and length, fault current or overcurrent will not think this is only 10mm so it should be fine.This interests me. Parallel conductors of different CSA. They will be parallel for about 10mm, connected to the same earth bar 10mm apart...would that be awful?
It does indeed, but over two terminals with mm between them even with a 43-57 split of probably 10mm or so maximum is it really going to cause an issue. Whilst I agree that it not best practice and as I suggested earlier a pin lug would be the best option, when In a fix it is a practical solution, and as Dusty says better than giving the conductor a haircut.It suggests the conductor is oversized to enable suitable termination as per manufacturer recommendations. You have also divided the conductor into separate unequal csas.
It may well not cause an issue but it creates parallel conductors of differing csa the length is not relevant. The suggestion of a swa core and sheath is totally different.It does indeed, but over two terminals with mm between them even with a 43-57 split of probably 10mm or so maximum is it really going to cause an issue. Whilst I agree that it not best practice and as I suggested earlier a pin lug would be the best option, when In a fix it is a practical solution, and as Dusty says better than giving the conductor a haircut.
If you use an SWA cable with 1 core and the armor both used as earth then there will be a difference in the size of earth conductor for the whole circuit and unequal current under fault can flow.
the voice of reason speaks. my tuppence worth is that you have a copper core cpc and a steel armour also as cpc. their respective resistances can never be the same, so the same size argument can't be applied. tin hat firmly wedged over lug holes.Terminating four strands of a 7-strand conductor in one terminal and three in another does not equate to creating parallel conductors in the conventional sense. Two paralleled cores of a cable need to be equal to ensure predictable current sharing where the CCC and adiabatic fault withstand capability are determined by the thermal and electrical characteristics of the cable. Within 10mm of the terminal bar, the thermal characteristics of the bar swamp those of the cable, while the electrical characteristics of the main cable length swamp those of the termination. Therefore provided both terminations are sound and can be relied upon to remain sound, the split termination will be 'better' than all conductors in one hole because both the electrical and thermal contact resistance are likely to be lower.
Notice I am not referencing the regulations here, only the physics.
If the copper cable is able to meet all limits for adiabatic, etc, on its own then you don't have to consider the parallel SWA there.the voice of reason speaks. my tuppence worth is that you have a copper core cpc and a steel armour also as cpc. their respective resistances can never be the same, so the same size argument can't be applied. tin hat firmly wedged over lug holes.
The OP was talking about the sheath and core as far as I can tell.It may well not cause an issue but it creates parallel conductors of differing csa the length is not relevant. The suggestion of a swa core and sheath is totally different.