Fitted a Consumer unit last week all was fine until kast night. Guy called me up saying lights in kitchen n living room flickers n went out. He says MCBs didn't trip but when he trips switch manually power to lights stay on.
Havnt been round yet but I'm thinking reverse polarity? Except wouldn't that have showed up in my Ze testing?
 
Get round there and have a look, it's amazing how the description offered by a customer gets distorted over the telephone!

Crossed polarity on the supply would have shown on your Ze test, Circuit crossed polarity would have shown on an R1+R2 test and Zs test.

Let us know the outcome!
 
ES don't you mean BC or are you not located in the UK

ES = Eddison Screw
SES = Small Eddison Screw
BC = Bayonet Cap

All available in the uk

Hows the db set out, are the lights on one rcd by themselves?
He says MCBs didn't trip but when he trips switch manually power to lights stay on.
Does he mean the mcb just resets ok or the lights are actualy comming on now?

Two options for me
A) as above, RCD tripped & customer hasnt reset it.
B) you didn't tighten the mcb's to the busbar (and this would be my first check).
 
Last edited by a moderator:
Each light is on a separate split board RCD. And yes ES I meant Edison Screw. Spoke to the customer,turns out he didn't isolate both at once just each one separate. So after calling him (unable to get to his) and advising to turn both off than on separately to determine that they can be isolated.......it turns out they can. It seems the radial supplying lights on the right isde of his house (both upstairs and down) has no lights working in any room.

So now my first initial feeling is loose connection.
 
Each light is on a separate split board RCD. And yes ES I meant Edison Screw. Spoke to the customer,turns out he didn't isolate both at once just each one separate. So after calling him (unable to get to his) and advising to turn both off than on separately to determine that they can be isolated.......it turns out they can. It seems the radial supplying lights on the right isde of his house (both upstairs and down) has no lights working in any room.

So now my first initial feeling is loose connection.
 
Spoke to the customer,turns out he didn't isolate both at once just each one separate. So after calling him (unable to get to his) and advising to turn both off than on separately to determine that they can be isolated.......it turns out they can.

That's what I meant by the story getting distorted by the customer, happens quite often!

With any luck, it'll be a failed mcb, sounds much better than a loose connection to the customer! (assuming you confess!)
 

Reply to What's happened? in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
696
davesparks
D
The challenge that you have with this is that you've no confirmed start point. Because you have a lack of an EICR you don't actually know what...
Replies
7
Views
606

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top