J
jmtisme
Was working with a heating engineer when I started cross bonding the pipework he laughed and said I should check the regs as cross bonding is no longer required. I looked at him then said something about British gas and water pipes not sure what his point was can anyone enlighten me??
If the cct is covered by rcd and disconnection times are met and another condition in the brb then supp bonding can be omitted
In that case the heating engineer is correct,there is no requirement in the BRB to supplementary bond heating pipes unless they are entering a special location and the 3 requirements to omit are not met.
Main bonding to heating pipes would only be required if they are extraneous conductive parts....
main bonding is always req supp bonding ommited under certain circumstances, if no rcd then yes supp bonds shall need to be in place
The installation is not protected by RCD so I think bonding is required ?
You said the pipework boiler is in a basement....supplementary bonding is only required in special locations as defined in the BRB.....There is no requirement for supplementary bonding/cross bonding in other locations regardless of RCD protection.
I'm going to be blunt here, I never cease to be staggered by the number of electricians on this forum and elsewhere who do not understand the requirements for bonding,it's such a simple concept yet results in more confusion and incorrect statements than any other subject.
Supplementary equipotential bonding is required in some locations and installations of bs7671 (PART 7 SPECIAL LOCATIONS)
if the installation meets the requirements for earthing and MAIN bonding there is no specific requirement for supp bonding of:
kitchen pipes/ sinks, boiler pipework, metallic pipes to wash basins, locations containing a bath or shower.
just read later post, bonds not in special location
However there is nothing wrong with providing supp bonding anywhere (although not a bs7671 requirement) so you could say you prefer to cross bond anyways and still tell him where to go, although i wouldnt advise getting into an argument if you dont fully understand what regs actually state.
What's he on about
Thread Tags
jmtisme,
ezzzekiel,