Supplementary equipotential bonding is required in some locations and installations of bs7671 (PART 7 SPECIAL LOCATIONS)
if the installation meets the requirements for earthing and MAIN bonding there is no specific requirement for supp bonding of:
kitchen pipes/ sinks, boiler pipework, metallic pipes to wash basins, locations containing a bath or shower.
just read later post, bonds not in special location
However there is nothing wrong with providing supp bonding anywhere (although not a bs7671 requirement) so you could say you prefer to cross bond anyways and still tell him where to go, although i wouldnt advise getting into an argument if you dont fully understand what regs actually state.