Was working with a heating engineer when I started cross bonding the pipework he laughed and said I should check the regs as cross bonding is no longer required. I looked at him then said something about British gas and water pipes not sure what his point was can anyone enlighten me??
 
If the cct is covered by rcd and disconnection times are met and another condition in the brb then supp bonding can be omitted
 
In that case the heating engineer is correct,there is no requirement in the BRB to supplementary bond heating pipes unless they are entering a special location and the 3 requirements to omit are not met.
Main bonding to heating pipes would only be required if they are extraneous conductive parts....
 
main bonding is always req supp bonding ommited under certain circumstances, if no rcd then yes supp bonds shall need to be in place
 
The installation is not protected by RCD so I think bonding is required ?

You said the pipework boiler is in a basement....supplementary bonding is only required in special locations as defined in the BRB.....There is no requirement for supplementary bonding/cross bonding in other locations regardless of RCD protection.

I'm going to be blunt here, I never cease to be staggered by the number of electricians on this forum and elsewhere who do not understand the requirements for bonding,it's such a simple concept yet results in more confusion and incorrect statements than any other subject.
 
Supplementary equipotential bonding is required in some locations and installations of bs7671 (PART 7 SPECIAL LOCATIONS)
if the installation meets the requirements for earthing and MAIN bonding there is no specific requirement for supp bonding of:
kitchen pipes/ sinks, boiler pipework, metallic pipes to wash basins, locations containing a bath or shower.


just read later post, bonds not in special location
However there is nothing wrong with providing supp bonding anywhere (although not a bs7671 requirement) so you could say you prefer to cross bond anyways and still tell him where to go, although i wouldnt advise getting into an argument if you dont fully understand what regs actually state.
 
Last edited by a moderator:
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
What's he on about
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
12

Thread Tags

Advert

Thread statistics

Created
jmtisme,
Last reply from
ezzzekiel,
Replies
12
Views
1,782

Advert

Back
Top