Would entering each RCD as a line on the schedule of test results be correct? If so, what would be entered in boxes such as Zs?
 
Use N/A for not applicable.

If I’ve got a split board, then top line is rcd1 with the rating, trip time etc.. then circuits 1,2,3,4,5 for example. Then another unnumbered line with rcd2, followed by circuits 6,7,8,9….

I find it pointless repeating the same trip times on 5 lines for each of the individual circuits
 
Use N/A for not applicable.

If I’ve got a split board, then top line is rcd1 with the rating, trip time etc.. then circuits 1,2,3,4,5 for example. Then another unnumbered line with rcd2, followed by circuits 6,7,8,9….

I find it pointless repeating the same trip times on 5 lines for each of the individual circuits
Cheers, this is what I have done previously.
 
Nothing is right or wrong provided it is clear.
I’ve not been on here for while hope you are all fine and well?

When recording the trip times I only record the x5 highest value (both sides of waveform) where the rcd is being used as additional protection. However if rcd is used as fault protection I then record the highest value at x1 (both sides of waveform) is this ok?

I don’t repeat this time for all circuits I normally put RCD 1 then list circuits below and then RCD 2 with circuits below that and record the above just on the RCD section.
 
I’ve not been on here for while hope you are all fine and well?

When recording the trip times I only record the x5 highest value (both sides of waveform) where the rcd is being used as additional protection. However if rcd is used as fault protection I then record the highest value at x1 (both sides of waveform) is this ok?

I don’t repeat this time for all circuits I normally put RCD 1 then list circuits below and then RCD 2 with circuits below that and record the above just on the RCD section.
Hello stranger. Just 1X for either additional or fault protection now. It changed with the new amendment.
 

Reply to What’s the correct way to enter RCD’s on a split load board on a schedule of test results? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
264
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
756
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
740

Similar threads

Ok I’ll try this when I’m down
Replies
4
Views
382
L
  • Question
My Understanding is the 6 Months interval is IET Guidance and this wording is incorporated onto the label which is a requirement in 514.12.2 where...
Replies
9
Views
641

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top