I keep seeing these on pics of installations, mostly industrial, and just wonder what they're for? Are they fused?

Why put one in when we can go straight to the breaker instead?
 
It is a good way to joint the cables from outside the cabinet to inside it.
they are not fused (normally) but can be.

example, I build a panel to control 5 pumps
there are various float switches and pressure sensors involved plus of course 5 x 3 phase pumps to connect.

it is far easier to build a panel with all the terminals marked and at the bottom of the panel for someone else to wire up to than it would be for the installer to have to wire all the sensors and motor cables to the relevant contactors and plc inputs inside the panel.
 
There are many reasons why but, in general they are used often in Panels Boards that are designed , built and tested off-site. When on-site the electrician can then gland and terminate all remote cables to the relevant terminal block. This saves the electrician pulling the panel board apart to locate its upstream connection point, which may be a breaker or overload or contactor. They are provide a good isolation point for testing and fault finding.
 
Just to add another advantage of the DIN terminals that you can link the terminals together using purpose designed jumper bars and that can be useful if you need, say, 4 cables connected to one without wanting to double-up wires, etc.

Also normally the green/yellow terminals have a clamp to the metal rail, and that is often useful for reliable low-impedance earthing. Of course there are some situations where you don't want that, like extending cables where you want to test the CPCs separately, but for panel building that is not so common.
 

Reply to What's the point of DIN rail terminal blocks? in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
376
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
944
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Sticky
Hi Richard, thanks for your comment. The relay is rated 12A peak. It's also worth noting that a relay contact will perform differently depending...
    • Like
    • Winner
Replies
4
Views
3K
When I was on the electric board We had a pair of pillocks connect a housing estate to a very large genset, the n lead was in two parts and not...
2
Replies
28
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top