When can an RCD be omitted from a domestic cable run | on ElectriciansForums

Discuss When can an RCD be omitted from a domestic cable run in the Domestic Electrician Forum area at ElectriciansForums.net

At any time.
There is currently no requirement to provide RCD protection for cables, other than those that make up a circuit for a location containing a bath or shower.
What about cables concealed below surfaces less than 50mm?
 
There is no requirement for them to be provided with RCD protection.
They do need an Additional protection Unless adequately protected from penetration from nails/screws or the like cables also require additional protection when ran in a wall containing metal parts i.e a stud partition wall with metal framework
 
If not protected by earthed metal sheath trunking or conduit at less than 50mm RCD required then
Earthed metallic sheath, earthed trunking or conduit, mechanically protected, be part of a SELV or PELV circuit or run in a prescribed route and provided with RCD protection.

Similar rules apply if if the wall’s internal construction includes metallic parts.
 
Earthed metallic sheath, earthed trunking or conduit, mechanically protected, be part of a SELV or PELV circuit or run in a prescribed route and provided with RCD protection.

Similar rules apply if if the wall’s internal construction includes metallic parts.

For those of you who think there is a requirement for RCD protection, you should learn to read.
It’s an option.
If you choose that option, it’s your choice, no one is twisting your arm forcing you to make that choice.
Oh and once again, I’ll point out that RCD protection is not an option for cables concealed above ceilings and below floors.
 

Reply to When can an RCD be omitted from a domestic cable run in the Domestic Electrician Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
250
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
723
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
695

Similar threads

Hi All, In need of some advice on what is and isn't allowed under regs. I'm extending a circuit in my house so I can install a socket on the...
Replies
0
Views
209
See there is the problem. I can put back to way it was. Is it safe, in my opinion NO!! It's wasn't safe before the incident. No Fused Spur...
Replies
9
Views
513

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top