Just been testing some sheltered schemes with lengthy Ring Mains for Corridor Sockets returning high Z's, original install 30+ years using MEM 3871 Type 3 mcb's struggling to meet 80%. Sockets used for low current i.e. Cleaning Equipment, scooter charging etc Replacement mcb's through Eaton ÂŁ 70+ each so been replacing with spare 10A mcb's to raise max value.

Can this same method be used if there is a break in the ring thats hard to trace. Surely lowering the mcb size to 20A or 16A takes away the ring requirement as the 2.5mm cannot be overloaded ?

Any flaws with the above ?
 
problem there is that if you can't find the break, you could be leaving live cable ends floating around. as long as you can make the radials safe. i.e. end each one at a socket, then OK.
 
A ring is always a ring if wired in a ring configuration, regardless of the MCB supplying it. I recently went to a job that the ring was part wired in 1.5mm cable, wasn't an option to rewire so MCB downrated to suit and recommendation to rewire, however it's still a ring now albeit a 10A ring.

When a ring is more than 100m it is still a ring, it's just a non compliant ring, or so I believe
 
A ring is always a ring if wired in a ring configuration, regardless of the MCB supplying it. I recently went to a job that the ring was part wired in 1.5mm cable, wasn't an option to rewire so MCB downrated to suit and recommendation to rewire, however it's still a ring now albeit a 10A ring.

When a ring is more than 100m it is still a ring, it's just a non compliant ring, or so I believe

A ring can can be longer than 100m, have a maximum area of 100 sq metres and still be compliant as long as the CSA of the cable does not permit the vd to fall below 5% of the supply voltage.
 
A ring can can be longer than 100m, have a maximum area of 100 sq metres and still be compliant as long as the CSA of the cable does not permit the vd to fall below 5% of the supply voltage.

I thought the reg, about a ring must not cover an area more than 100M squared was done away with?
 

Reply to When is a Ring not a Ring ? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
311
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
834
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
936

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top