Just been testing some sheltered schemes with lengthy Ring Mains for Corridor Sockets returning high Z's, original install 30+ years using MEM 3871 Type 3 mcb's struggling to meet 80%. Sockets used for low current i.e. Cleaning Equipment, scooter charging etc Replacement mcb's through Eaton ÂŁ 70+ each so been replacing with spare 10A mcb's to raise max value.
Can this same method be used if there is a break in the ring thats hard to trace. Surely lowering the mcb size to 20A or 16A takes away the ring requirement as the 2.5mm cannot be overloaded ?
Any flaws with the above ?
Can this same method be used if there is a break in the ring thats hard to trace. Surely lowering the mcb size to 20A or 16A takes away the ring requirement as the 2.5mm cannot be overloaded ?
Any flaws with the above ?