N

nlbhoy

I've had to run a 25mm 3core swa from meter (outside) to DB about 8m away, do I need to fit
a switch fuse or isolator switch in meter box?

Or does this only apply to meter tails more than 3m?

Thanks in advance
 
you dont need a fuse isolator switch..fuse isolator switch needed just when you have under 25mm cable..in every home dno supply its 100a who its suitable for 25mm swa or 25mm tails..if you run a 16mm swa you have to have fuse isolator switch after meter with the fuse suitable for this size of conductors..in your situation its not necessary..for isolator switch its two different situation..if the meter its already fix you don't need to have isolator switch..if the meter its not fix yet and you waiting for suppliers to come and fix again its on two diferent situation..if you call EDF they not asking you for isoator switch .they dont mind if you have or dont have switch isolator..if you call British Gas they fixed their own switch isolator after meter where you fix your swa or tails..

The DNO specific the maximum length of conductor which may be connected to their service fuse, for any cable longer than that a distribution circuit needs to be installed. The size of the cable is irrelevant, it is the length which matters. This is backed up in the regulations by the requirement that cables not protected by a suitable fuse should not be longer than 3m (the service fuse is not there to protect consumers cables and must not be treated as such)

Apologies if I have misunderstood your post at all, but it is very difficult to understand. Could you please make the effort to write in coherent English please.
 
davesparks or others may be able answer a query I have on the sizing of fuses in such situations.

Lets say the DNO fuse is a 1361 Type 2 100amp, and the switch fuse would be say a Wylex with BS 88-2 fuse (I think) with 25mm tails, total load would not exceed 80amp.

What would be the correct size of fuse to put in the customers isolator, 80amp or 100amp. I only ask, because I have asked previously, and been advised to use either arguments being;

select 100amp cos, you will not be able to predict which would go first in fault, and would deprive installation of 100amp supply should that be required retrospectively or

80amp cos that would provide discrimination with the DNO fuse.
 
davesparks or others may be able answer a query I have on the sizing of fuses in such situations.

Lets say the DNO fuse is a 1361 Type 2 100amp, and the switch fuse would be say a Wylex with BS 88-2 fuse (I think) with 25mm tails, total load would not exceed 80amp.

What would be the correct size of fuse to put in the customers isolator, 80amp or 100amp. I only ask, because I have asked previously, and been advised to use either arguments being;

select 100amp cos, you will not be able to predict which would go first in fault, and would deprive installation of 100amp supply should that be required retrospectively or

80amp cos that would provide discrimination with the DNO fuse.

For the purpose of the installation you can ignore the service fuse as it is not yours and cannot be used to provide protection to any part of the installation.
This does lead to the ridiculous situation that you can end up with two fuses of the same rating in series, but from a theoretical/regs point of view there is only the consumers fuse there.
If you wanted to discriminate fully with the DNO fuse then I believe you'd need to be installing no more than a 40A fuse downstream of it, but may be wrong on that.
However the service fuse does have different characteristics to the HRC you would be fitting in a switchfuse (unless it's a KMF type switchfuse which uses service fuses)

The bottom line is that you should design your distribution circuit in its own right as you would any other circuit in your installation. So establish your design current, then select your ocpd rating to suit.

The last time I did this in a house was for a small bungalow which I ran a 63A submain.
 

Reply to When To Fit Switch Fuse/Isolator in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
376
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
944
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Replies
7
Views
511
I would hazard a guess your electrician may be able to contact your DNO and have the switch swapped to a MFS very quickly..
Replies
13
Views
656

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top