Do you apply the periodic inspection and test label after a CU change? (No EICR)

  • Yes, always.

    Votes: 4 66.7%
  • It depends.

    Votes: 2 33.3%
  • Never.

    Votes: 0 0.0%

  • Total voters
    6

HandySparks

-
Mentor
Arms
Joined
Jul 22, 2011
Messages
4,333
Reaction score
2,656
Location
Hampshire
BS7671 Amdt 1, 514.12.1 says:
A notice .... shall be fixed ... upon completion of the work carried out in accordance with Chapter 61 [initial verification] or 62 [periodic inspection and testing]. "Important, This installation should be periodically inspected and tested ... Date of last inspection, Recommended date of next inspection".

Clearly, if you've just done a full EICR or a whole new installation, then the label is required. But what about a modification or addition to the instalation? What about just a couple of new circuits in an extension? What about a new CU?

At my assessment for joining ELECSA, I changed the CU in my own house. I queried the point with the assessor, who said that in this case the label was required. If I had done a full EICR prior to the CU change, I would have agreed with him; as it is, I'm not so sure.

Do you apply the label but write on it the extent of the new/changed part of the installation?
 
I would apply the label in the case of a CU change, as you will have had to T&I all of the circuits you have re-connected.

I rarely fill out a formal EICR form on a CU change, unless the customer explicitly requests one, the EIC can be used in lieu for certification purposes, and in most cases the EIC has everything and more than the EICR has where a CU change has occurred.
 
I also have doubts about when this is required.
I would say that if I am making an alteration addition to an existing installation AND the installation has an existing label then my putting on a new label would delay (unless I used the same date as the old label) an inspection of the previous circuits so I would not use a new label.
If there is no label on the existing installation then I would (except once when I forgot!) put a label on, specifying the work done.

For a CU change (where the label is now gone) or a rewire then I would say a new label is required, possibly.:rolleyes4:
 
The label itself is irrelevant, what is relevant is any certificates or reports.

However, I've always thought a good idea would be an extra box on the label where you could write details of what the label refers to eg W6 and W7, whole installation etc
 

Reply to When to use the periodic inspection and testing label? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
317
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
842
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
965

Similar threads

  • Question
No it is not implying it is safe, it is stating what the recommended date for the next inspection is. The next inspection date sticker doesn't...
Replies
10
Views
2K
davesparks
D
  • Question
My older card has it but my newer card doesn’t
    • Like
Replies
1
Views
740

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top