Where do you stop with this rcd malarkey?

I'm wiring a mates house at the minute which will be supplied from a tt system. The suppliers meter will be resessed into the outside wall. The consumer unit's will be located in a utility room some seven or eight meters away. They'll be supplied by a split con centric cable run in an underground duct. I'll have about 13 or 14 circuits (big house) which i'll split over two consumer units. So i'm thinking i'll need a 30 ma rcd protecting the underground cable, a 30 ma rcd protecting the cu supplying the sockets, cooker etc, a 30 ma rcd protecting the cu supplying the lights, heating etc and then 2 seperate 30 ma rcd's protecting the fire alarms and fridge/freezer. Thats 5 30 ma rcd's i'll need to cut down on inconvenience if something trips. Your thoughts would be helpful.
 
i think youll need two dual split load consumer units, the submains dont need a rcd!
You sure the sub mains dont neen an rcd? I thought as they were under ground and a tt system with the lenght being about 8 meters they would need to be rcd. I'm also installing a 80 amp fuse switch to protect the sub mains.
 
You sure the sub mains dont neen an rcd? I thought as they were under ground and a tt system with the lenght being about 8 meters they would need to be rcd. I'm also installing a 80 amp fuse switch to protect the sub mains.
Put a 100mA at the other side of your switchfuse that will protect the cable and you have to do it for a tt anyways:D
 
Hi
100ma RCD does not discriminate against a 30ma RCD thus not complying to 17th Edition Regs . Personally i would opt for a 100ma Time Delayed incoming RCD controlling 5 zones made up of maybe 2 RCD's & 3 RCBO's as most manufacturers offer High Integrity CU's now.
 
whats the Ze at panel?? a 200ma main rcd for supply as long at ZexIn<50 then split 5d.b with 30ma for final circuits
remember the 50v mximum for fault voltage it will also give you discrimminaton
Basic discrimmination rule is miss 1 size
 
Hi
100ma RCD does not discriminate against a 30ma RCD thus not complying to 17th Edition Regs . Personally i would opt for a 100ma Time Delayed incoming RCD controlling 5 zones made up of maybe 2 RCD's & 3 RCBO's as most manufacturers offer High Integrity CU's now.


Why do you say there is no discrimination between the 30mA and 100 mA?
 
Hi
100ma RCD does not discriminate against a 30ma RCD thus not complying to 17th Edition Regs . Personally i would opt for a 100ma Time Delayed incoming RCD controlling 5 zones made up of maybe 2 RCD's & 3 RCBO's as most manufacturers offer High Integrity CU's now.

How do you make that out? the 30mA would trip before the 100mA would'nt it?
 
I agree an 100ma time delay pre distribution circuits to the 2 CU's and protect those cables with a switch fuse. Then a std split rcd board(s) as required, the second board can be fed from a mcb in the first board if required or its own switch fuse. I assume the 2 boards are some distance appart.
NB check that the IxV<50V (as per previous post).
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Advert

Thread statistics

Created
hoover,
Last reply from
andekoch,
Replies
11
Views
1,918

Advert

Back
Top