I'm wiring a mates house at the minute which will be supplied from a tt system. The suppliers meter will be resessed into the outside wall. The consumer unit's will be located in a utility room some seven or eight meters away. They'll be supplied by a split con centric cable run in an underground duct. I'll have about 13 or 14 circuits (big house) which i'll split over two consumer units. So i'm thinking i'll need a 30 ma rcd protecting the underground cable, a 30 ma rcd protecting the cu supplying the sockets, cooker etc, a 30 ma rcd protecting the cu supplying the lights, heating etc and then 2 seperate 30 ma rcd's protecting the fire alarms and fridge/freezer. Thats 5 30 ma rcd's i'll need to cut down on inconvenience if something trips. Your thoughts would be helpful.
 
i think youll need two dual split load consumer units, the submains dont need a rcd!
You sure the sub mains dont neen an rcd? I thought as they were under ground and a tt system with the lenght being about 8 meters they would need to be rcd. I'm also installing a 80 amp fuse switch to protect the sub mains.
 
You sure the sub mains dont neen an rcd? I thought as they were under ground and a tt system with the lenght being about 8 meters they would need to be rcd. I'm also installing a 80 amp fuse switch to protect the sub mains.
Put a 100mA at the other side of your switchfuse that will protect the cable and you have to do it for a tt anyways:D
 
Hi
100ma RCD does not discriminate against a 30ma RCD thus not complying to 17th Edition Regs . Personally i would opt for a 100ma Time Delayed incoming RCD controlling 5 zones made up of maybe 2 RCD's & 3 RCBO's as most manufacturers offer High Integrity CU's now.
 
whats the Ze at panel?? a 200ma main rcd for supply as long at ZexIn<50 then split 5d.b with 30ma for final circuits
remember the 50v mximum for fault voltage it will also give you discrimminaton
Basic discrimmination rule is miss 1 size
 
Hi
100ma RCD does not discriminate against a 30ma RCD thus not complying to 17th Edition Regs . Personally i would opt for a 100ma Time Delayed incoming RCD controlling 5 zones made up of maybe 2 RCD's & 3 RCBO's as most manufacturers offer High Integrity CU's now.


Why do you say there is no discrimination between the 30mA and 100 mA?
 
Hi
100ma RCD does not discriminate against a 30ma RCD thus not complying to 17th Edition Regs . Personally i would opt for a 100ma Time Delayed incoming RCD controlling 5 zones made up of maybe 2 RCD's & 3 RCBO's as most manufacturers offer High Integrity CU's now.

How do you make that out? the 30mA would trip before the 100mA would'nt it?
 
I agree an 100ma time delay pre distribution circuits to the 2 CU's and protect those cables with a switch fuse. Then a std split rcd board(s) as required, the second board can be fed from a mcb in the first board if required or its own switch fuse. I assume the 2 boards are some distance appart.
NB check that the IxV<50V (as per previous post).
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined

Thread Information

Title
Where do you stop with this rcd malarkey?
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
11
Unsolved
--

Advert

Thread statistics

Created
hoover,
Last reply from
andekoch,
Replies
11
Views
1,917

Advert

Back
Top