About to re sit testing section of am2. Am I required to test phase rotation at the incoming switch and also the 3 phase socket and motor. Just can't seem to find any clear instructions on what they expect on this test
 
Not sure if this applies to AM2.
The phase sequence on the 3 phase installation would affect the rotation of the motor on the motor supply circuit
You will be required to select the appropriate Phase Sequence tester and perform a test at the Main Switch and at the motor connections.
Both tests should indicate the same phase sequence.
 
Last edited:
Not sure if this applies to AM2.
The phase sequence on the 3 phase installation would affect the rotation of the motor on the motor supply circuit
You will be required to select the appropriate Phase Sequence tester and perform a test at the Main Switch and at the motor connections.
Both tests should indicate the same phase sequence.
Thanks for the response really appreciate it, so that's kinda what I was thinking aswell for the test points and hoping someone would say the same. Ill be using the multifunctional megger tester they provide which has phase rotation onit
 

Reply to Where do you test from in phase rotation test on am2 in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
459
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

  • Question
That looks like a Metrel display (I have one), they have a permanent 3 wire display that measures the three combinations so I would say that’s a...
Replies
5
Views
795
Having some issues with my companys fluke 1662/1663 tester. Zeroing 2 leads for continuity test we get the value 0.08 which is expected. The issue...
Replies
0
Views
288

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top