I have my sceme assessor coming today so am just brushing up on all the regs with regards the job he will be looking at.

Does anyone know where in the regs it says that 16mm tails are ok with a cut out fuse of 60A?

Thanks all :smile5:
 
just basic knowledge here. the CCC of 16mm is approx. 87A. protected by a 60A fuse, then Iz > In, so compliance is achieved.
 
If you are referrring to an existing installation, and you know that the DNO fuse is 60A there is NO REQUIREMENT to fit 25mm tails.

Simply look up the cable requirements for 60A and you'll see that 16mm is OK.

The point being is that neither the OSG or BGB state 25mm tails are required - but because the OSG shows 25mm in the pickies, people think its a reg.

If its a new build or rewire you could be in deep poo poo as the DNO's do recommend 25mm..... that said I'm not sure that the assessor will even comment.
 
Thanks both of you. Thought it might be written in black and white, but you're quite right, it should be more than enough to point the assessor towards the current carrying capacities of 16mm.

No, it not a new build Murdoch :sweatdrop:
 
All as above, I would just add if say you fitted a new cu 100amp dp switch, the "assessor" might want you to put 25mm tails in to match cu max demand, weather it be 60amp or 100amp cutout.
 
All as above, I would just add if say you fitted a new cu 100amp dp switch, the "assessor" might want you to put 25mm tails in to match cu max demand, weather it be 60amp or 100amp cutout.

if an assessor tried that one on me he would get a good arguement! There is no connection between the rating of the main switch and the maximum demand.........
 
Mr M, Hope you are well. Long time no see.

I think this is what you are thinking of, despite the rambings:

16mm2 tails with a 100a cut out are ok if the MD of the installation(div & load inc) does not exceed the ccc of the tails. 434.5.2 must be met. easy peasy lemon squeezy.

cr.ed.
 
I fitted a domestic DB recently with 10mm tails and was within BS7671 .... Ill let you newbies ponder that one ...... (Dont spoil my fun! @ the Regular experienced members) :thinking2:
 
Last edited by a moderator:
Near enough if the upfront devices i.e. the overload protection of the circuit(s) limits the max demand on the tails then the tails may be reduced.

2way DB with a 40amp and a 10amp mcb's will not demand more than 50amp under normal conditions so no need to tail with 16mm or 25mm
If spare ways exist then you shouldn't be practicing this method its for situations where design load has already een set and can't be added to.
 

Reply to where in the regs does it say 16mm Tails are ok? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
305
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
825
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
916

Similar threads

  • Question
Yeh that’s my thinking. I have to supply the box so can order a bigger 3 phase option to give myself a bit more room
Replies
3
Views
848
In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top